Thread: Support of Luminaires in suspended ceilings

  1. #1

    Support of Luminaires in suspended ceilings

    I would like some opinions on the support of luminaires in suspended ceilings. 2008 NEC, 410.36 states; "Luminaires shall be securely fastened to the ceiling framing member by mechanical means such as bolts, screws, or rivets. Listed clips identified for use with the type of ceiling framing member(s) and luminaire(s) shall also be permitted. Are the bend out "clips" on the fixtures considered a "listed clip"? Would you have to see spec. sheets for each type of fixture to determine if they are "listed"? What do you think?

  2. #2
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,465
    I have never failed an inspection using them.

  3. #3
    Join Date
    Jun 2005
    Location
    North Logan, Utah
    Posts
    7,939
    The bend out clips if used properly would be OK.

    Keep in mind that in some areas with seismic requirements that you might need independent support wires in addition to the clips on the fixture.

    Chris

  4. #4
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,465
    Quote Originally Posted by raider1 View Post
    The bend out clips if used properly would be OK.

    Keep in mind that in some areas with seismic requirements that you might need independent support wires in addition to the clips on the fixture.

    Chris
    Whoops! I thought that the OP was talking about just connecting the fixture to the grid, not supporting it. I read the entire code section that was partly quoted and I change my reply. In my area additional support wires are required unless you can prove that the grid is listed as support for light fixtures. The support wires are to be marked as to distinguish them as fixture supports. Two wires per fixture on a diagonal. The clips are only used as stabilizers for maintenance on the fixture.

  5. #5
    Join Date
    Jan 2008
    Location
    New York City
    Posts
    406
    Quote Originally Posted by jumper View Post
    Whoops! I thought that the OP was talking about just connecting the fixture to the grid, not supporting it. I read the entire code section that was partly quoted and I change my reply. In my area additional support wires are required unless you can prove that the grid is listed as support for light fixtures. The support wires are to be marked as to distinguish them as fixture supports. Two wires per fixture on a diagonal. The clips are only used as stabilizers for maintenance on the fixture.
    Do you use Chains to support the fixture?

  6. #6
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,465
    Quote Originally Posted by DARUSA View Post
    Do you use Chains to support the fixture?
    Sometimes, if specs require it. Mostly I use grid wire that I partially spray paint for identification purposes for the inspector.

  7. #7
    In our area lay in light fixtures are sufficiently secured using the bend out clips but some clients/buildings/architects require chains to the deck. Many electricians will say that it's code to use the chains...however the "hurricane" clips as we call them sufficiently meet the code requirement.

  8. #8
    Join Date
    Jan 2007
    Location
    New Jersey
    Posts
    834
    The fixtures are UL approved with the installation instructions identifying the clips as the mounting method to the grid. This is NEC code compliant but seismic issues may have your building codes requiring additional support. I work in a state divided into two seismic areas with the north requiring additional support and the south does not.
    Rick Napier
    Inspector and Instructor

  9. #9
    Join Date
    Apr 2007
    Posts
    848
    We are allowed to screw the fixtures to the "mains" as long as they were run the right way. Or use the clips or tie wires. I usally have a crew screw them in when lamping the fixtures.

  10. #10
    Join Date
    Aug 2007
    Location
    Broward Co.
    Posts
    361
    In Broward/Dade/Palm Beach I always put spray painted ceiling ties from the trusses caddy corner to the light, and 4 screws through the grid into the light. You'll never fail an inspection for fixture support doing it this way, remember to clip your MC to your own ties and not the grid guys.