    direct tv

    Dish was installed when i bought the house. In the process of getting all coax cable off the side of the house putting it in the crawl space and comming up in a wall. On one side of the house there is a block with 2 pieces of coax comming from dish and 2 pieces leaving going to 2 different rooms but theres a piece of #12 green comes off this block and is stuck in the ground. Dont under stand what this ground is doing . does the dish need to be grounded the other 2 rooms in the house dont have this set up. Guess thats what you get when you get a free install and holes in the side of the house. Looked at direct tv web site didnt see any thing about this issue .Whats the proper way to ground the dish or does it even need one.

  2. #2
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    304
    It should be grounded to the building service where it enters. If the dish is not located in the vicinity of service, it's should be grounded via ground rod not just a wire sticking in the ground.. at the closest earth point. Then from that rod, the conductor needs to be routed to the main service and terminated properly.
    Now is the only time you own. Live, love, toil with a will. Place no faith in time for the clock may soon be still.

  3. #3
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,645
    Here is an article you might find useful:

    http://ecmweb.com/mag/electric_dish_...ful_satellite/

  4. #4
    Join Date
    Aug 2008
    Location
    bumpass,Va
    Posts
    35
    I thank they forgot a few steps. Like i said the only ground i see comes off that coax splitter and #12 off that stuck in the ground. i hit it with the weed eater. So how come that line of work gets away with doing half ass work and no insp and call it a free install. What are you grounding the metal arm that holds the dish cause the dish is fiberglass i thank i havent got up there and looked to close its mounted up on the side of the house. Know that im not working i have plenty of time to fix it right. thanks

  5. #5
    Join Date
    Dec 2005
    Location
    WI & AZ
    Posts
    1,965
    Quote Originally Posted by TwinCitySparky View Post
    it's should be grounded via ground rod not just a wire sticking in the ground.. at the closest earth point. Then from that rod, the conductor needs to be routed to the main service and terminated properly.
    I agree it needs to be bonded to the GES via a #6 but what purpose would the ground rod serve:confused:
    Tom

    " And all the science I don't understand, it's just my job five days a week "