Thread: Megger operation / circuit paramaters

  1. #1
    Join Date
    Oct 2009
    Posts
    172

    Megger operation / circuit paramaters

    I started to ask some questions in a previous post regarding megger operation but I figured I'd start a new thread to ask more specific questions.

    Specifically I wanted to understand exactly how a megger functioned and how to reperestent the different parts of a megger with circuit equivelents.

    So looking at my 1000V AMEC 1040 megger I notice that for 1000V DC it has a nominal output current of 1mA and a measurement range of up to 2000Mohms.

    From the previous post it was stated that the current output in a megger is current limited and in my case it appears that its limited to 1mA. What is it that limits this output current to 1mA at 1000V? Output impedance?

    I believe a Megger works by outputting this 1mA output current and measuring the voltage drop between leads in order to calculate a resistance? So does the unit always output 1mA regardless of what the measured circuit resistance is? What if measured circuit is a dead short?

    It was also mentioned in previous post that voltage on measured circuit may be less than 1000V due to voltage drop across megger output. So when measuring at circuit does the primary point of the circuit actually see 1000V or is it less depending on output impedance and current?

    I have seen some cases where when measuring a circuit the voltage will not increase, on an adjustable megger and will stay at a miniumum voltage. What is happening here? Is there not enough voltage in these cases to push the current?

    I also assume that DC is used for this instrument to avoid issues with capacitance coupling in circuits.

  2. #2
    Join Date
    Oct 2009
    Posts
    172
    Does anyone know where I can find any information on this?

  3. #3
    Join Date
    Jul 2008
    Location
    way north
    Posts
    1,261
    I did a google search on "megger circuits". There were a bunch. Here's one"
    http://www.allaboutcircuits.com/vol_1/chpt_8/7.html

    cf

  4. #4
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,354
    Quote Originally Posted by Pitt123 View Post
    I started to ask some questions in a previous post regarding megger operation but I figured I'd start a new thread to ask more specific questions.

    Specifically I wanted to understand exactly how a megger functioned and how to reperestent the different parts of a megger with circuit equivelents.
    You have a DC source powering a series circuit with the load and a calibrated resistor, the voltage drop is measured across the resistor. Knowing the source voltage, voltage drop, and current the meter does the math for you

    As seen my attached sketch your “Ohmmeter” is actually measuring current. The meter applies a test voltage and measures the current flow through the circuit and uses Ohms law to calculate resistance which is displayed on the meter in Ohms. If the applied voltage is not high enough, the amount of current passed through the resistance is below the sensitivity range of the meter.

    Ohm meters are connected to a component which is removed from the circuit, Ro is an adjustable resistor whose purpose is to zero the ohm meter and correct for battery aging. It is also a current-limiting resistor which includes the meter resistance Rm. Zeroing the ohm meter is accomplished by shorting the ohm meter terminals and adjusting Ro to give full-scale deflection; this is done automatically by modern digital ohmmeters.

    When the unknown resistance Rx is connected across the ohm meter terminals, the current is measured by calculating the total series resistance. Using the following equation:

    I= V/ (RO+RX)

    A digital ohmmeter will automatically do this calculation for you while an analog meter reading 0 ohms will cause full meter deflection. The meter face says ohms, but it is actually indicating amps, therefore full deflection (All the way to the right) will indicate 0 ohms while a reading of near 0 amps will cause little reflection of the meter and indicate near infinite resistance. (There is also no such thing as infinite resistance but we will save that argument for future discussion)

    For digital displays, if the applied voltage of the circuit under test is not high enough to cause enough current flow through the circuit for the meter to sense, the display will read “O.L”. Contrary to popular belief, this does not mean overload, it means “Outside Limits”, in other words, the measured current flow is below the sensitivity capabilities of the meter.

    The only real difference with a Megohmeter is the test voltage and ratings of the resitor, the same concepts apply as I described above for digital and analog Megohmeters.

    Quote Originally Posted by Pitt123 View Post
    So looking at my 1000V AMEC 1040 megger I notice that for 1000V DC it has a nominal output current of 1mA and a measurement range of up to 2000Mohms.

    From the previous post it was stated that the current output in a megger is current limited and in my case it appears that its limited to 1mA. What is it that limits this output current to 1mA at 1000V? Output impedance?
    1Ma is the max output at that voltage, based on the power supply, which also determines the max reading you can read. In your case yours will have current too low to measure (Accurately) when you have >2G of resistance. Your megger displaying >2G is the same as your ohmeter displaying "O.L."

    Quote Originally Posted by Pitt123 View Post
    I believe a Megger works by outputting this 1mA output current and measuring the voltage drop between leads in order to calculate a resistance? So does the unit always output 1mA regardless of what the measured circuit resistance is? What if measured circuit is a dead short?
    I think I answered the 1st part of this above. The current will vary depending on the resistance of the circuit, current is what the meter uses as the variable to calclate resistance.

    Quote Originally Posted by Pitt123 View Post
    I have seen some cases where when measuring a circuit the voltage will not increase, on an adjustable megger and will stay at a miniumum voltage. What is happening here? Is there not enough voltage in these cases to push the current?

    There are 3 currents being measured, leakage current, capacitive charging current, and absorbtion current (See 2nd attachment). Leakage current should stay the same over time, the other 2 will decay with the decay rate depending on the type of and condition of the equipment you are testing. As the current decays the meter output voltage tends to creep up at times before correctiing itself. The rate of these decays is calulated to determine the Polarization Index and Dielectric Absorbtion Ratio of the insulation. The PI and DAR are key indicators of the overall condition of the insulation of inductive equipment such as transformers and rotating equipment.

    Hope this helps, I tried to keep it basic so all you EE's don't need to nitpick, we can start another thread if you want to get all EE on me
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Ohmeter.png 
Views:	80 
Size:	4.3 KB 
ID:	4209  
    Attached Images Attached Images

  5. #5
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,354
    Quote Originally Posted by Cold Fusion View Post
    I did a google search on "megger circuits". There were a bunch. Here's one"
    http://www.allaboutcircuits.com/vol_1/chpt_8/7.html

    cf
    Hmmm, that seems easier than the whole write up I just did.

  6. #6
    Join Date
    Jul 2008
    Location
    way north
    Posts
    1,261
    Quote Originally Posted by zog View Post
    Hmmm, that seems easier than the whole write up I just did.
    Well, the pictures make it easier for the EEs

    cf

  7. #7
    Join Date
    Jun 2007
    Location
    Warren, MI
    Posts
    881
    Quote Originally Posted by zog View Post
    1Ma is the max output at that voltage, based on the power supply, which also determines the max reading you can read. In your case yours will have current too low to measure (Accurately) when you have >2G of resistance. Your megger displaying >2G is the same as your ohmeter displaying "O.L."
    Since 2G is the max for the AEMC 1040, anything over that shows "OL" just like a ohmeter.

    A max. of 1ma at 1000V is the same spec for the AEMC 1050/1060 which at 1000V goes up to 4T. Are you saying that 1ma is inadequate? As I recall, don't you own either a 1050 or 1060 and have often recomended the AEMC brand?
    Bill

  8. #8
    Join Date
    Jan 2008
    Posts
    7,427
    Quote Originally Posted by Cold Fusion View Post
    Well, the pictures make it easier for the EEs

    cf
    But without text using Crayola, we still can't get it.:grin:
    BB+/BB=?

  9. #9
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,354
    Quote Originally Posted by wptski View Post
    Since 2G is the max for the AEMC 1040, anything over that shows "OL" just like a ohmeter.

    A max. of 1ma at 1000V is the same spec for the AEMC 1050/1060 which at 1000V goes up to 4T. Are you saying that 1ma is inadequate? As I recall, don't you own either a 1050 or 1060 and have often recomended the AEMC brand?
    My AEMC never says O.L., just >4T, which is rare. The 1060 has a larger power supply which is why it has a 1mA output with a 4T load compared to 2G.

    And yes, AEMC is my Megohmeter of choice. But I also use a Megger for big jobs with hundreds of tests needed so I can export the data right to my test reports in Power Db.

  10. #10
    Join Date
    Jun 2007
    Location
    Warren, MI
    Posts
    881
    Quote Originally Posted by zog View Post
    My AEMC never says O.L., just >4T, which is rare. The 1060 has a larger power supply which is why it has a 1mA output with a 4T load compared to 2G.

    And yes, AEMC is my Megohmeter of choice. But I also use a Megger for big jobs with hundreds of tests needed so I can export the data right to my test reports in Power Db.
    The 1040 does show "OL" but the 1050/1060's screen will blink or flash which is a "out of range" error or equal to "OL".
    Bill