Gas clothes dryer and 210.52

Status
Not open for further replies.

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Our resi guy called today and asked if a laundy room with a gas dryer would still require a 30A outlet for an electric dryer. I called a well respected member of this Forum that is up on dwellings and he agrees that its not required.

After further review and not enough time tonight to pursue this myself, I turn to you for conformation.

This is what I don't quite grasp.

210.11 Branch Circuits Required.

Branch circuits for lighting and for appliances, including motor-operated appliances, shall be provided to supply the loads calculated in accordance with 220.10. In addition, branch circuits shall be provided for specific loads not covered by 220.10 where required elsewhere in this Code and for dwelling unit loads as specified in 210.11(C).
220.10 General.

Branch-circuit loads shall be calculated as shown in 220.12, 220.14, and 220.16.
220.14 Other Loads ? All Occupancies.

(B) Electric Dryers and Household Electric Cooking Appliances. Load calculations shall be permitted as specified in 220.54 for electric dryers and in 220.55 for electric ranges and other cooking appliances.
Required or not? All this appears to me to be calculated if present.

Thanks
 

Cavie

Senior Member
Location
SW Florida
210.50 Outlets required. (F) Laundry Areas. One receptical outlet required. No mention of dryer outlet required. Gas or Electric.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
A bigger question. Where did you find a well respected MEMBER of this Forum. Isn't that not an oxymoron ?:grin:
 

kbsparky

Senior Member
Location
Delmarva, USA
220.14 Other Loads ? All Occupancies.

(B) Electric Dryers and Household Electric Cooking Appliances. Load calculations shall be permitted as specified in 220.54 for electric dryers and in 220.55 for electric ranges and other cooking appliances.

Since this code section is dealing with Electric dryers, it does not apply to your situation.

You don't need a separate circuit for an electric dryer when you are outfitting the laundry room for a gas dryer.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
A bigger question. Where did you find a well respected MEMBER of this Forum. Isn't that not an oxymoron ?:grin:

Ok so maybe not. It was Ken, but I have a great deal of respect for him. He still owes me 6 bucks for the cokes I bought him in Chicago but given his advice today I will call us square.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Our resi guy called today and asked if a laundy room with a gas dryer would still require a 30A outlet for an electric dryer.

Required or not? All this appears to me to be calculated if present.
I'd say the same applies to laundry and kitchen. We're not required to install a range circuit if it's piped for gas, but we're certainly allowed to if the customer perfers the option.

Personally, I'd want both. I've had a Jenn-Air dual-fuel range in the past, and when the gas range we have now dies, that's what we'll replace it with. There is a range receptacle.
 

jumper

Senior Member
In the 1960's of los angeles the EC would install outlets for Electric cooking and outlet for electric dryer and the plumbers would provide gas hook ups. just in case the homeowner prefered on over the other

It was and is still a good idea.

I'd say the same applies to laundry and kitchen. We're not required to install a range circuit if it's piped for gas, but we're certainly allowed to if the customer perfers the option.

Personally, I'd want both. I've had a Jenn-Air dual-fuel range in the past, and when the gas range we have now dies, that's what we'll replace it with. There is a range receptacle.

Me too. I would try and sell the customer on the idea of running the circuit now if future access is limited. The reason is that many people are very picky about these appliances.

My co-worker has all gas appliances, except for the dryer. He just does not like them.

As for a range circuit, yes to running it also.

My wife is a baker and insists on a electric oven, she believes it bakes more evenly than gas.

I am a wild eyed wanna be chef and want gas for instant temperature control. I can not stand waiting for cook top elements to heat up or cool down.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I always run a 10/3 nm w/ gr. even for a gas dryer. I use it as an upsell stating that some people may want electric down the road. It is amazing how easy an add on it can be.
 