garage area?

Status
Not open for further replies.

wireman1

Senior Member
in a garage area of a auto dealership where they service cars the west wall part of that area is classified class1 div2 all wiring in that area is run over head. on the east wall of the same area there is a distance of 50 ft. between east and west wall is the area on the east wall still classified class 1 div 2 ? they may want to mount a sub panel on this wall and it might be less than 24 in from finish floor please site any articles which may apply to this situation thanks
 

kwired

Electron manager
Location
NE Nebraska
in a garage area of a auto dealership where they service cars the west wall part of that area is classified class1 div2 all wiring in that area is run over head. on the east wall of the same area there is a distance of 50 ft. between east and west wall is the area on the east wall still classified class 1 div 2 ? they may want to mount a sub panel on this wall and it might be less than 24 in from finish floor please site any articles which may apply to this situation thanks
Have you read through Art 511?

Unless there is fuel dispensing, paint booth/paint handling most classified areas are limited to just the first 18 inches above the floor and in last couple NEC editions they have relaxed some situations a little by making a distinction between major and minor repair facilities.
 