Thread: Doble Testing?

  1. #1
    Join Date
    Feb 2005
    Location
    BF PA
    Posts
    493

    Doble Testing?

    can anyone give a brief statement about this or point me to an article? Not coming up with much on the GOOGLE

  2. #2
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,368
    Quote Originally Posted by khixxx View Post
    can anyone give a brief statement about this or point me to an article? Not coming up with much on the GOOGLE
    There is not really such thing, just slang. It refers to a Power Factor/Dissapation Factor test done on mostly transformers but also motors and MV cables. Doble makes the most commonly used test equipment for these tests. Hence the name Doble test.

    Just like a Megger test, which is really an Insulation Resistance test, but Megger is the most common brand name equipment.

  3. #3
    Join Date
    Jul 2009
    Location
    Ware Shoals, South Carolina
    Posts
    1,085
    Doble test could also refer ( slang ) to a timing test for a breaker with a shunt trip. Doble made early equipment for this also. It measured the time from the moment the trip signal was initiated until the contacts opened.

  4. #4
    Join Date
    May 2005
    Location
    Redmond, WA
    Posts
    783
    Another name is insulation power factor test.

    Doble equipment puts a 2.5 kV or 10 kV AC signal on the transformer or other test specimen, then carefully measures signals proportional to the watts and VA. From that you can calculate, or read directly on the fancier instruments, the power factor of the current flowing into the insulation. A perfect insulation only has capacitive current flowing, power factor zero. Wet, dirty or degraded insulation will have resistive leakage current, raising the power factor. 1% or lower is good, but like megger readings a lot is relative.

    A true Doble test sequence makes several measurements, similar to the megger readings on a transformer: Hi & Lo to gnd, Lo to Hi & gnd, Hi to Lo & Gnd plus others with guard inputs. A lot of care is needed to get accurate readings and to accurately adjust for temperature and other factors. Doble supplied a data base of readings for all the transformers tested with their equipment. That gave the customer something to compare his readings too on a unit of a similar size, type and manufacture.
    Bob Wilson

  5. #5
    Join Date
    Aug 2008
    Location
    Cape Cod
    Posts
    26
    Just reading replies. Saw your reply. My question is " I shouldn't let my romex hang in the bed of my pickup all year and get soaked

  6. #6
    Join Date
    Feb 2005
    Location
    BF PA
    Posts
    493
    Thanks, This clears things up a bit.