    Question Are Challenger and SQ-D QO Breakers Interchangeable?
    Does anyone have any information on, or know if Challenger and Square-D QO type circuit breakers are interchangeable? They look very similar.
    Thanks
  2. #2
    Join Date
    Jul 2007
    Posts
    3,100
    Do you mean Square D Homeline? QO has a totally different stab.
  3. #3
    Join Date
    May 2003
    Posts
    1,201
    Quote Originally Posted by David40 View Post
    Thanks
    The only breakers that interchange w/ QO are Cutler-Hammer & Siemens UL classified QO replacements, if someone is a hack they can FUBAR a Cutler-Hammer type CH breaker into a QO loadcenter, since they are the same width & clip on the bus stab in the same way but clip onto the panel interior differently.
    A Challenger or a SQ D HO line are 1" in width compared to a QO is 3/4", which makes it impossible to interchange them.
  4. #4
    Now that I think of it I think it is Cutler-Hammer not Challenger. I have a ton of the QO laying around and I'd like to use them up instead of having to buy a new Cutler-Hammer breaker on those rare occasions where I run into a Cutler-Hammer panel. Is it easier to get a QO into a Cutler-Hammer panel than the other way around?
  5. #5
    Join Date
    Apr 2007
    Posts
    848
    Cutler Hammer has CH and BR both are different in the way they mount.
    A Challenger is a BR style breaker
    The more I learn the less I seem to know....
  6. #6
    Join Date
    Jul 2007
    Posts
    3,100
    You will regret it.
  7. #7
    Join Date
    Feb 2003
    San Francisco Bay area
    Posts
    649
    Cutler-Hammer has 'classified' breakers that have been UL tested and 'classified' to be put into a SQ D QO panel...however, I know of no such classification for SQ D breakers being classified to put into other mfr's panels.
  8. #8
    Join Date
    Feb 2003
    Wisconsin
    Posts
    9,812
    The manufacturer of the breaker says do not do it. Square D does not 'approve' of having any of their breakers installed into any other manufacturer's panels.
    Just because you can, doesn't mean you should.