    FLA vs. FLC
    Can anybody tell me the difference between the FLA vs FLC.
  2. #2
    Join Date
    Jun 2005
    Logan, Utah
    Posts
    8,200
    FLA= Full Load Amps
    FLC= Full Load Current
    They basically mean the same thing.
    Chris
  3. #3
    Join Date
    Dec 2008
    Macon,GA
    Posts
    200
    They are the same, Full Load Current = Full Load Amps. I see FLC when referring to OCPD and FLA when speaking of equipment.
  4. #4
    Join Date
    Jul 2006
    Posts
    7,639
    Semantics, i.e. how they are used in a sentence. Example:
    My motor has an FLC of 28A.
    But saying "My motor has an FLA of 29A" is being redundant because "amps" is already implied by the acronym "FLA". If I say "The FLA of my motor is 28" I am being technically correct, but it sounds odd.
  5. #5
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    22,767
    Quote Originally Posted by Jraef View Post
    That's like AC current and DC current, PIN numbers and VIN numbers, and LCD displays.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  6. #6
    Join Date
    Sep 2008
    UK
    Posts
    11,224
    Quote Originally Posted by LarryFine View Post
    Tautological perhaps?
    :grin:
  7. #7
    Join Date
    Jan 2008
    Posts
    8,955
    Quote Originally Posted by Besoeker View Post
    :grin:
    Needless tautological redundancy. :grin:
    BB+/BB=?
  8. #8
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    The one I notice a lot at work is EMS system or BAS system.
    'We were contracted to install the Energy Management System System'
  9. #9
    Join Date
    Nov 2007
    Columbus, Ohio
    Posts
    2,234
    Or like saying L.B.F. is a fine electrician. :grin:
  10. #10
    Join Date
    Nov 2007
    massachusetts
    Posts
    3,166
    FLC is used when you size breaker size and wire size for motors.
    FLA (located on the motor) is used to size overload protection for motors
    the tables in 430 part XIV are FLC and what you need to size circuit ampacity
    read 430.51 and 430.31
    FLA and FLC mean the same thing for the most part. but in the real world the FLA of the motor is always less than the FLC in the tables.