Commercial Bathroom Receptacle on Ltg. Ckt ?

Status
Not open for further replies.

flashlight

Senior Member
Location
NY, NY
Occupation
Electrician, semi-retired
I know that a receptacle is not required in a commercial bathroom
but if installed requires GFI per 210.8(B)

But, if installed, does it require its own circuit or to be on a circuit that does
not power anything else but the bathroom ?

I can't find where it's not permitted to add a GFI receptacle (at commercial customer's request) that gets power from a circuit that powers a few lights and a couple of outlets in restaurant dining area. Load is very light, so that would not be a problem. Running a new circuit would be cost prohibitive.
 

480sparky

Senior Member
Location
Iowegia
210.11(C)3 requires a dedicated circuit for dwellings. There is no similar article for commercial use.

winner.gif
 

480sparky

Senior Member
Location
Iowegia
No, I'm serious, I was testing to see if I can get a different font.:grin:

You can use a limited amount of fonts that the forum software supports when you post. I think the default is Veranda, but there's about 20 you can choose from, none of which are very exciting.
 