100A feeder
Toros
Tujunga, CA
Hi
For my friend
on the plan
i have indicated 100a cit breaker through #3 wire thhn cu @75 deg for 130 feet feeder supplying the tenant sub panel
he said code has changed recently and we need #2 tbhn cu
is it true???
Hi
For my friend
on the plan
is it true???
In the 2014 NEC, #3cu is still rated 100A @ 75deg.
... he said code has changed recently...
The only code change that I can think of that would be relevant is the provision for reduced ampacity for a service or feeder which supplies the entire load of a dwelling unit. In [2011] Table 310.15(B)(7) shows that for 100A calculated current you can use #4 copper.
The standard wire capacity table (no more than three wires in a conduit), 310.15(B)(16), shows that 100A requires #3 if you are allowed to use the 75C rating.
In [2014] the first table is no longer present, but the text tells you that you can use a conductor with only 83% of the calculated required ampacity after applying adjustments and corrections. The results are exactly the same except that [2011] is not explicitly clear about the need to apply adjustments and corrections to the sizing in the table. The second table, 310.15(B)(16), is as far as I can see identical between {2011] and [2014].
I guess you are assuming that since the breaker is 100A the calculated load must be less than or equal to that?
Hi
For my friend on the plan i have indicated 100a cit breaker through #3 wire thhn cu @75 deg for 130 feet feeder supplying the tenant sub panel he said code has changed recently and we need #2 tbhn cu is it true???
No code change so the answer is no.:)
Hi
For my friend
on the plan
is it true???
#3 Cu is correct, as long as:
1. Terminals on both sides are listed and labeled for 75C
2. Wire is listed and labeled for 75C or greater
3. You aren't using NM cable AKA romex
4. No derate factors apply
The energy code could limit the voltage drop along this feeder, which could result in a larger required wire size.
But nobody pays any attention to those energy codes :)