For years, when replacing a panel, I have spliced too short egc's together and extended them to the ground bar using largest size conductor. An inspector objected to this today. I see no prohibition in code. Any thoughts?
pete m.
Ohio
Ask the inspector for the code section.
Pete
GoldDigger
Placerville, CA, USA
Retired PV System Designer
He may be confusing the prohibition on reversible splices or connections on a Ground Electrode Conductor (GEC). If you are replacing a main panel you will have to make sure that either the GEC fits or that you use an irreversible compression spice to extend it. (Not likely you would want to use Cadweld for this purpose. :))
JFletcher
Williamsburg, VA
Are you combined grounds of different circuits then bringing them down to the ground buss via one wire? wag, but if so, tho I dont have a code section, I'm thinking if said hypothetical connection fails it would leave multiple circuits ungrounded, or he's objecting to the wire size of the pigtailed grounding wire.
infinity
New Jersey
Journeyman Electrician