Generator Installation

Status
Not open for further replies.

ernric43

Member
Location
United States
I'm looking at installing a single phase 240V generator. We want to have the entire building backed up by the generator. Does code require a means of disconnect between the utility and the ATS?
I'm seen several examples of installations with a mix of results.

Thanks,
Rich
 

iwire

Moderator
Staff member
Location
Massachusetts
The NEC prohibits ATS on the supply side of the service disconnect. See 230.80 or close to that for details

That leaves a couple of choices

Either put the ATS on the load side of the service disconnect or use a service rated ATS and that becomes the service disconnect.
 