I am feeding a trailer, (pull behind. ) From a 60 amp generator to a 60 amp panel. Separate ground and neutral from generator to panel, does the ground and neutral have to be separate and why and what section in the nec

Sent from my SM-G360P using Tapatalk
 

tom baker

First Chief Moderator
Staff member
Please review 250.20, 250.30, 250.34 and 250.35.
If the generator is a SDS, then you need a SBJ, where depends on the generator OCPD location.
With the generator, just like a service, you need grounding, bonding,a bonding jumper, and a grounding electrode system if its a SDS.
 

Joseph mulherin

Inactive, Email Never Verified
Location
blythe,ga 30805
Can someone recommend a grounding electrode idea for this trailer, has a 60 amp generator feeding a 60 amp panel, how would you do the grounding

Sent from my SM-G360P using Tapatalk
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Can someone recommend a grounding electrode idea for this trailer, has a 60 amp generator feeding a 60 amp panel, how would you do the grounding

Sent from my SM-G360P using Tapatalk

You can always drive a ground rod, but IMO your question can't be answered with the information you have given. Did you review the code sections Tom posted.
 