    Arc-fault
    Arc faults are now required in WI. 210.12B which referes to branch circuits suplying outlets do they mean just recepticles? Are lighting outlets or lighting circuits required to be arc fault protected? I take it an unfinished basement would not require arc fault protection? And why not kitchen outlets? They way I read it tamper proof recepticles are pretty much required in the whole house? Thanks
  2. #2
    Join Date
    Jul 2007
    Iowegia
    Posts
    16,632
    Branch circuits start at the terminal of the breaker. AFCI protection is required for the entire circuit.... conductors, devices, luminaires, smoke detectors included.
  3. #3
    Join Date
    Aug 2006
    Cape Cod, Massachusetts
    Posts
    615
    Quote Originally Posted by arnettda View Post
    The key word there is outlets meaning lights, plugs. I know in Massachusetts they are not required for outside lights, kitchens, unfinished basements, and bathrooms as well. As for TR they are required in the whole dwelling and outside receptacles must be TR/WP.
  4. #4
    Join Date
    Feb 2003
    Wisconsin
    Posts
    7,988
    Arc-Fault in all interior living areas, not in unfinished basement or kitchen.
    Yes, lighting and smoke circuits need arc fault.
    Do you ever go to the website for WI's building codes?
    http://www.commerce.wi.gov/sb/SB-Ele...msProgram.html
    Just because you can, doesn't mean you should.