When installing wires in parallel, can you use one lug for termination, or do you have to use a splitter lug so that both wires are not on one lug.
If yes or no, where in nec
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree. Your most applicable Code references would be 110.3(B) and 110.14(A)
"Terminals for more than one conductor and terminals used to connect aluminum shall be so identified."
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's a photo of parallel conductor terminations and one of a lug listed for two conductors.
20080209_58.JPG

Rob%27s%20Work%20022.JPG
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
There are probably not many lugs that could handle 2- 1/0 conductors. That is the minimum size you could use with a few exceptions.
 