    Do you need to allow for the working space in 110.26 for a non fused safety switch?
    Specifically for a disconnect for an AC drycooler?
    This is a 480 volt nonfused disconnect. (not a disco)
    This would be a condition 2 that would require 3'6" of clearance.
    I believe that it needs the proper clearance and headroom.
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices
  2. #2
    Join Date
    Nov 2007
    Columbus, Ohio
    Posts
    2,234
    Quote Originally Posted by tkb View Post
    I feel that it is likely to be examined while energized.
    If that is so, then yes.
  3. #3
    Quote Originally Posted by Volta View Post
    I agree with Volta, but what do you mean by "(not a disco)" when you're referring to a disconnect?
  4. #4
    Join Date
    Jul 2003
    MA
    Posts
    2,053
    I mean a disconnect.
    A disco to me needs a mirrored silver ball.
    The term is so residential.
    Tim
    Master Electrician
    New England
  5. #5
    Join Date
    Jan 2009
    ORLANDO FLA
    Posts
    1,282
    Well yes .
    Would you need a clearance in front of a transformer ?
    No fuses in it ?
    But you check voltage to service it or you might open it up to test or check lugs or grounding connections if you had a problem so yes to me anything electrical needs space in front .
    Ive got a question how about a 4 square box ?
  6. #6