Thread: GFCI Protection of Garbage Disposal Receptacle

  1. #1
    Join Date
    Sep 2007
    Location
    Omaha, NE
    Posts
    105

    GFCI Protection of Garbage Disposal Receptacle

    In a commercial breakroom which does not meet the definition of a kitchen, what is the consensus on whether a NEMA 5-20R receptacle installed under a sink to serve a garbage disposal requires GFCI protection? Is the area in the base cabinet under a sink considered to be "within 1.8 m (6 ft) of the outside edge of the sink"?
    Jason Rohe, P.E.

  2. #2
    Join Date
    Jun 2005
    Location
    North Logan, Utah
    Posts
    7,939
    Yes, the garbage disposal receptacle would be within 6' of the edge of the sink IMHO, and would require GFCI protection under the 2008 NEC in accordance with 210.8(B)(5).

    Chris

  3. #3
    Join Date
    Jul 2007
    Posts
    189
    If you plugged in a hair dryer with a six foot cord in that outlet, could you drop it in the sink? :grin:

  4. #4
    Under 2008 I would agree with Chris, bu under 05' the 6' rule does not apply to "other than dwelling units"

  5. #5
    Join Date
    Jul 2004
    Location
    Ca and Wa
    Posts
    1,486

    GFCI-Disposer

    Quote Originally Posted by jrohe View Post
    In a commercial breakroom which does not meet the definition of a kitchen, what is the consensus on whether a NEMA 5-20R receptacle installed under a sink to serve a garbage disposal requires GFCI protection? Is the area in the base cabinet under a sink considered to be "within 1.8 m (6 ft) of the outside edge of the sink"?
    Be aware that commercial disposers 230V rated do not require a GFCI.
    rbj, Seattle...Safety is a Professional Courtesy.

  6. #6
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    5,698
    Quote Originally Posted by Keri_WW View Post
    If you plugged in a hair dryer with a six foot cord in that outlet, could you drop it in the sink? :grin:
    Someone that would wait until their hair was in the sink to dry it probably could.

    I was going to put a smiley there, then realized that there are people out there that would do something like that.
    Cheers and Stay Safe,

    Marky the Sparky

  7. #7
    Join Date
    Mar 2004
    Location
    Collier County (Naples), Florida, USA
    Posts
    55
    Quote Originally Posted by jrohe View Post
    In a commercial breakroom which does not meet the definition of a kitchen, what is the consensus on whether a NEMA 5-20R receptacle installed under a sink to serve a garbage disposal requires GFCI protection? Is the area in the base cabinet under a sink considered to be "within 1.8 m (6 ft) of the outside edge of the sink"?
    I would say if the base cabinets have doors on them, separating "the path of string" from the receptacle and the sink, then no GFCI is required.

  8. #8
    Join Date
    Dec 2005
    Location
    WI & AZ
    Posts
    1,960
    Quote Originally Posted by davidaengelhart View Post
    I would say if the base cabinets have doors on them, separating "the path of string" from the receptacle and the sink, then no GFCI is required.
    I would tend to agree but as cheap as GFI recepts are, I'd put one in to be sure.
    Tom

    " And all the science I don't understand, it's just my job five days a week "

  9. #9
    Join Date
    Jan 2009
    Location
    Easton, Maryland NEC: 2011
    Posts
    7,465
    Quote Originally Posted by davidaengelhart View Post
    I would say if the base cabinets have doors on them, separating "the path of string" from the receptacle and the sink, then no GFCI is required.
    Sorry, but I gotta disagree. The code simply says 6' from a sink. IMO that means the AHJ can say it has to be GFCI.
    "Electricity is really just organized lightning." George Carlin


    Derék

  10. #10
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    16,828
    Quote Originally Posted by davidaengelhart View Post
    I would say if the base cabinets have doors on them, separating "the path of string" from the receptacle and the sink, then no GFCI is required.
    Tell us more about this 'path of string' theory.