Thread: Ground bar bonding to breaker box

  1. #1
    Join Date
    Feb 2004
    Posts
    142

    Ground bar bonding to breaker box

    What does code say about the need of bonding the equipment ground bar to the chassis of the breaker box on a sub-panel, that is connected to the main with EMT conduit?

  2. #2
    Join Date
    Nov 2007
    Location
    Columbus, Ohio
    Posts
    2,234
    NEC says "Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any equipment grounding conductor(s) associated with those circuit conductors shall be connected within the box or to the box with devices suitable for the use ..." 250.148.

    Even better, in case someone feels that a panelboard enclosure isn't a box , is 408.40. "... The terminal bar shall be bonded to the cabinet and panelboard frame, if of metal, ..."

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    26,418
    Quote Originally Posted by hardworker View Post
    What does code say about the need of bonding the equipment ground bar to the chassis of the breaker box on a sub-panel, that is connected to the main with EMT conduit?
    If this is an equipment ground bar then the screws that are provided with the accessory will suffice to bond the bar to the box. If you are using EMT then there is no need to include an egc-- if that is what you are asking.

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,256
    Quote Originally Posted by Volta View Post
    Even better, in case someone feels that a panelboard enclosure isn't a box , is 408.40. "... The terminal bar shall be bonded to the cabinet and panelboard frame, if of metal, ..."

    We all know that by definition it isn't.

    It's a cabinet.
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  5. #5
    Join Date
    Nov 2007
    Location
    Columbus, Ohio
    Posts
    2,234
    Quote Originally Posted by infinity View Post
    We all know that by definition it isn't.

    It's a cabinet.
    I don't disagree . . . much :grin:.

    Having some trouble finding that definition of box, though. :confused: .

    I do see where a panelboard shall be mounted in "cabinets, cutout boxes, or enclosures designed for the purpose ..." 408.38.

  6. #6
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    6,646
    There are two code articles for panels (the incorrect but widely used term)
    312 is the box
    408 is the guts
    Many electricians have only installed loadcenters, which are the box and guts together.
    Moderator-Washington State
    Ancora Imparo

  7. #7
    Join Date
    Feb 2004
    Posts
    142
    If the equipment ground bar is already factory installed in a panel, is it already bonded by the screws they used to factory install it or do you have to add some sort of bonding device to it?

  8. #8
    Join Date
    Nov 2007
    Location
    Columbus, Ohio
    Posts
    2,234
    Quote Originally Posted by hardworker View Post
    If the equipment ground bar is already factory installed in a panel, is it already bonded by the screws they used to factory install it or do you have to add some sort of bonding device to it?
    Already bonded by the mounting screws, unless it is a special case of an isolated ground bar 250.146(D).

  9. #9
    Join Date
    Oct 2008
    Location
    Brooklyn, NY
    Posts
    883
    Quote Originally Posted by hardworker View Post
    If the equipment ground bar is already factory installed in a panel, is it already bonded by the screws they used to factory install it or do you have to add some sort of bonding device to it?
    Check with the manufacturer. Chances are the bar is already bonded but it's good to be on the safe side.
    Eric Kench, P.E.


    If it's not broken don't fix it