Originally Posted by
erickench
Actually the GEC is located at the enclosure containing the system bonding jumper.
The problem here is that I came across an old diagram from the 1990s that shows an SBJ running from the transformer neutral to the EGC terminal bar located at the disconnect. If it's in separate enclosures then which enclosure do you connect the grounding electrode conductor?
The GEC is connected in the enclosure where the grounded and grounding conductors are connected to each other. The grounding and grounded conductors, in the case of a transformer, can be connected to each other at either the transformer or the OCPD, but not both. No mater where the GEC is connected, a bonding jumper will be required between the transformer and the OCPD.
Don, Illinois
"It is the first responsibility of every citizen to question authority." B Franklin