Isolation Transformer IG Connection

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Take a look at this schematic for an isolation transformer. Does the grounding setup meet the NEC? The current setup has all of those ground connections terminating on the XO and a bonding jumper going to the transformer case.
Isolated%20Ground%20connection.jpg
 

ty

Senior Member
Typically, the 'NEUTRAL' would be shown with a line drawn from the center of the 'Y', not to the 'Ground Electrode', Electrically it is the same, but not how it is typically drawn.

The 'Neutral Lift' on F, is just showing the Neutral and Isolated Ground not bonded to the Equipment groundon the secondary?
 

cadpoint

Senior Member
Location
Durham, NC
Typically, the 'NEUTRAL' would be shown with a line drawn from the center of the 'Y', not to the 'Ground Electrode', Electrically it is the same, but not how it is typically drawn.

The 'Neutral Lift' on F, is just showing the Neutral and Isolated Ground not bonded to the Equipment groundon the secondary?

Then it's a bad Drawing! And is a Basic Code Violation! Get this, As Drawn!
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The "F" is part of the drawing that got truncated. It actually was the word "Removable" for removable links.

I should mention that the "current setup" is what is actually installed but this drawing is what they really want.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The only odd thing I notice about the SDS grounding & bonding is that there is no discernible system bonding jumper.

Is the Main Service ungrounded ?

Nope, the main service is 277/480. My guess is that it was simply drawn that way to show the feeder for the primary without a neutral. This drawing is from an audio consultant for a transformer feeding sound equipment receptacles.

The question here is would the setup depicted in the drawing be any different electrically than if all of the terminations were at the XO with a bonding jumper to the case instead of all of the conductors terminating at a single point on the transformer case as shown?
.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
...
The question here is would the setup depicted in the drawing be any different electrically than if all of the terminations were at the XO with a bonding jumper to the case instead of all of the conductors terminating at a single point on the transformer case as shown?
.
I don't see where there would be any electrical difference. How are all of the conductors terminated at the single point on the case?
 

ty

Senior Member
This drawing is from an audio consultant for a transformer feeding sound equipment receptacles.

well there's your problem :)

The question here is would the setup depicted in the drawing be any different electrically than if all of the terminations were at the XO with a bonding jumper to the case instead of all of the conductors terminating at a single point on the transformer case as shown?
.

I don't think so.
 

cadpoint

Senior Member
Location
Durham, NC
Were reaaly talking about a lot of things :)

Section VI 250.110

But where also talking about this MH neutral 100 definations from ECM
711ecmCSfig1.jpg


I'm sorry I don't get the implied sepation on these two circuit lines, anything smart yes SDS or whatever otherwise no.

I can only recall a code but can't remember which one that if your going to switch the neutral you switch everything at once.

95% of electrician will never see that or use that, I just think its scarey to imply something that bad.
A box of rocks I might be, but that sybolism leaves a whole lot to be desired!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I don't see where there would be any electrical difference. How are all of the conductors terminated at the single point on the case?


That would require a small piece of bus bar with the appropriate sized lugs installed and bolted to the transformer case. IMO it's no different electrically than landing everything on the XO with a bonding jumper to the can.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The "F" is part of the drawing that got truncated. It actually was the word "Removable" for removable links. QUOTE]

I think he is refering to the removable links.

I agree electrically everything required to be grounded & bonded are.


Yes, that's what those pieces are in the bottom right of the drawing. Removable links for the neutral and IG conductors. The previous guy didn't install them as he debated that they serve no real purpose.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I can only recall a code but can't remember which one that if your going to switch the neutral you switch everything at once.

I must have missed something?
Where are we switching the Neutral??


The removable links worry me too. Why would you want a removable link in the neutral or ground connection? Is that something the audio guy added to the drawing? Is the audio guy going to remove these if he has ground noise in the audio system? Maybe he thinks he will remove these and then ground the system elsewhere.

Yes, that's what those pieces are in the bottom right of the drawing. Removable links for the neutral and IG conductors. The previous guy didn't install them as he debated that they serve no real purpose.

I think maybe the previous guy might have had the right idea. Not installing them might keep the audio guy from removing a required ground connection.