Generator Shared Load

Status
Not open for further replies.

Hameedulla-Ekhlas

Senior Member
Location
AFG
Greeting all,

There is a Main Distribution Panel which feeds 350kVA load. Two Generators 250kVA and 100kVA through a Automatic Transfer Switch are connected to this Main Distribution Panel. At peak load both generators are online or on duty.

Now my Question is,

Suppose, it is a peak load (350kVA) and both generators are online. Now what is the shared kVA of each generator for this peak load.

Can anybody advise me regarding this. How to do the calculation ?
 

Hameedulla-Ekhlas

Senior Member
Location
AFG
Greeting all,

There is a Main Distribution Panel which feeds 350kVA load. Two Generators 250kVA and 100kVA through a Automatic synchronize Transfer Switch are connected to this Main Distribution Panel. At peak load both generators are online or on duty.

Now my Question is,

Suppose, it is a peak load (350kVA) and both generators are online. Now what is the shared kVA of each generator for this peak load.

Can anybody advise me regarding this. How to do the calculation ?

I corrected the red line
 

ron

Senior Member
Depending on the load share module, they will either share up to their rating (or a percentage of), or attempt to share equally, so the smaller one will stall at 150kVA.
 