Thread: Insulating properties of air

  1. #1
    Join Date
    Nov 2008
    Posts
    106

    Insulating properties of air

    Is there a "rule of thumb" concerning the insulating properties of air? In other words is there something to go by such as 1000 volts needs 1" of clearance to ground? 480 volts = 1/2" to ground, etc?

  2. #2
    Join Date
    Dec 2004
    Location
    Fort Collins, CO NEC: 2011
    Posts
    15,319
    Can you be more specific about the particular installation being considered?

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    16,627
    I would think that the conductors movement ability and likely hood of foreign object contact would need to be considered in any clearances.

  4. #4
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,183
    If I understand correctly as to what you are looking for, you need to review the NESC (National Electric Safety Code) otherwise known as IEEE C2.
    "Just because you're paranoid, doesn't mean they're not out to get you"

  5. #5
    Join Date
    May 2005
    Location
    Barboursville, West Virginia
    Posts
    895
    Quote Originally Posted by Red Wiggler View Post
    Is there a "rule of thumb" concerning the insulating properties of air? In other words is there something to go by such as 1000 volts needs 1" of clearance to ground? 480 volts = 1/2" to ground, etc?
    I seem to remember that it takes 10,000 volts per inch to arc through normal air. That probably doesn't help, but if I had 1,000 volts I'd want a lot more than an inch of clearance. Things like humidity will change the properties of the air and decrease the arc threshold. I don't know of any official distances to follow, but the NESC would be a good place to look like king said.
    Engineers are always honest in matters of technology and human relationships. That's why it's a good idea to keep engineers away from customers, romantic interests, and anyone else who can't handle the truth.

  6. #6
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    4,449

  7. #7
    Join Date
    Nov 2008
    Posts
    106

    Insulating properties of air

    The reason for the question is just for my personal benefit. I was thinking of a situation where a conductor (Medium Voltage) improperly routed with in a section of gear in such a way that a section of the conductor is in contact with a of bus bar of a different phase. (Which I know is not an acceptable practice).

    I was hoping that I could find information (table) that says a conductor of whatever voltage should maintain X" from busing (sections of bus bar).

    1000 volts = 2"
    5000 volts = 5"
    xxxx volts = ?"

  8. #8
    Join Date
    Jan 2009
    Location
    ORLANDO FLA
    Posts
    1,234

    Dielectric breakdown

    Well read page 4-133 art 250. in the Standard Handbook for Electrical Engineers . There is a chapter on Paschen,s air density effects on dielectric strength . Read this very good and a chart and graphs !

    But hands on 1 inch can handle a lot more the 1000 volts but its all about what voltage at what pressure and whats between the charge points .

    This is just personal information below do not use this for you work i play with high voltage as a hobbie !

    Take 15000volts AC 1/4 inch gap it will cross at 1/2 of a inch it will not cross at 60 ma if you increase the freq it will be less and start to pass the gap at less distance between the points .

    When we test high voltage cables we rap the terminal ends with sandwich rap its very thin in mills but 70 000 volts ACwill not pass thur 4 raps of this thin layer .

    Now in free air at 30000 volts AC it will bleed of into the air you can hear it hissing you can see it spark the gap at 50000volts ac but it depends on many different conditions .


    Actually a air blast is used to stop a flow or spark in high voltage heat makes a good path for flow but a cool blast of air will put it out

    Take care
    Last edited by ohmhead; 05-22-10 at 06:22 AM.

  9. #9
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    46,973
    Quote Originally Posted by Red Wiggler View Post
    Is there a "rule of thumb" concerning the insulating properties of air? In other words is there something to go by such as 1000 volts needs 1" of clearance to ground? 480 volts = 1/2" to ground, etc?
    Check out NEC Table 408.56 for some info.

  10. #10
    Quote Originally Posted by ohmhead View Post
    Well read page 4-133 art 250. in the Standard Handbook for Electrical Engineers . There is a chapter on Paschen,s air density effects on dielectric strength . Read this very good and a chart and graphs !

    But hands on 1 inch can handle a lot more the 1000 volts but its all about what voltage at what pressure and whats between the charge points .

    This is just personal information below do not use this for you work i play with high voltage as a hobbie !

    Take 15000volts AC 1/4 inch gap it will cross at 1/2 of a inch it will not cross at 60 ma if you increase the freq it will be less and start to pass the gap at less distance between the points .

    When we test high voltage cables we rap the terminal ends with sandwich rap its very thin in mills but 70 000 volts ACwill not pass thur 4 raps of this thin layer .Now in free air at 30000 volts AC it will bleed of into the air you can hear it hissing you can see it spark the gap at 50000volts ac but it depends on many different conditions .


    Actually a air blast is used to stop a flow or spark in high voltage heat makes a good path for flow but a cool blast of air will put it out

    Take care
    I was once told that 10,000 vac would not pass through two wraps of 33. Okay Myth busters,,,is that for real?