    Replacement panel board height

    I have been asked to quote an exterior panel board and transformer replacement serving a foot ball field.

    The existing install is mounted to the back of the scoreboard about 10' above grade.

    In my efforts to make this replacement code compliant I have checked NEC 240.24 which restricts over current device to a height of 6'7". These breakers are serving the scoreboard, field lighting, some GFCI receptacles and a small concession stand.

    There are not used as switches.

    I checked NEC 600 if scoreboard would be classified as a sign but do not see any answer to my question there.

    I would think it would be practical to mount the panel and breakers at this height to prevent non-qualified personel from accessing and for physical protection.

    I just cannot seem to locate an exception to the breaker height.

    Am I missing something?

    I attached a photo.

    Thanks.
    Last edited by netaguy; 10-11-10 at 07:42 PM.

  2. #2
    Join Date
    Jun 2005
    Location
    North Logan, Utah
    Posts
    7,939
    The panelboard in your situation would need to be mounted with the breakers no higher than 6'7" to the highest breaker.

    The conditions listed in 240.24(A) that would allow the breaker to be higher would not apply to your situation I afraid.

    Chris

  3. #3
    Join Date
    Dec 2008
    Location
    Providence, RI
    Posts
    20
    Thanks for the reply, the panel will get lowered.

  4. #4
    Join Date
    Sep 2004
    Location
    Durham, NC
    Posts
    5,208
    Chris, I understand the Code height requirement!

    Don't you think they did this because of mischief and waived the height limit?
    If your even thirsty, your two quarts low.

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    18,110
    To keep mischevious persons out of the panel install a lock on the cover.

    Most outdoor panels have provisions for this.

  6. #6
    Join Date
    Jun 2005
    Location
    North Logan, Utah
    Posts
    7,939
    Quote Originally Posted by kwired View Post
    To keep mischevious persons out of the panel install a lock on the cover.

    Most outdoor panels have provisions for this.
    Agreed, there are much better ways to keep people out of an electrical panel that don't require that the panel be elevated.

    An elevated panel would increase the hazards involved when working in the panel.

    Chris