Originally Posted by
petersonra
Is this happening on startup? If so, it's possible the fan is moving when the VFD tries to start, and that can create a very high current. Usually the drive itself can do DC injection braking to keep the fan motionless when it is off.ETA:
Does this thing have an encoder on it?
I agree with peter. I had 2 100 HP air handlers on vfd's in a hospital surgery suite. When the power failed these motors would still be spooling down when the emergency generator picked up the non critical gear. I installed some time delay relays that also energized the braking feature upon transfer of power, both from normal to emergency but the other way too. Solved the problem.