Emergency Lights in bathrooms
jonny1982
CA
Are emergency lights required in bathrooms? In this case, the building is an activity center for girl scouts.
Thanks
Sent from my E6782 using Tapatalk
luckylerado
Thanks
I do not believe that you will find a code specifically calling out bathrooms however the illumination requirements of the "Means of Egress" as defined by NFPA 101 and IBC do apply to the path of travel which will include the space inside the bathroom. I believe that 1 FC min is required but check NFPA 101 and 2012 IBC section 1006
mgookin
Fort Myers, FL
Are emergency lights required in bathrooms? ...
Thanks
The NEC does not prescribe when EM lights are required. Those requirements come from building & life safety codes, which are local.
Call your local fire marshal and ask.
We always required them in windowless restrooms, but we are not in Cali.
iwire
Massachusetts
I wonder if they are following code or not?
Not required in most locations.
mgookin
Fort Myers, FL
I don't remember if we did that via local amendment or via an interpretation out of NFPA 101. The Fire Marshal's office would require it and the building department would do the permitting & inspections with the fire marshal inspecting their operation at time of final inspection and on annual inspections.
