Originally Posted by
walkerj
Well the wall type is clearly stated on the fire Marshall approved stamped drawings.
The wall type has been tested by ul in the exact manner we have on site.
We have proved this in writing, but she wants putty pads on all metal boxes installed in these 30' long walls, some with up to six 4" sq boxes.
Multiply that times forty walls on four floors and that is a lot of putty pads.
It is just so aggravating because the simplest solution would be to put in a 2x6 stud, but the owner will not accept that.
Open the NFPA 5000 and look up your wall type that you say has been tested. Right under that, it says these construction types are examples only, and due to constrcuction differences, the AHJ makes the final decision.
I was in your situation, and had to bow down gracefully and create an exit stratedgy to minimize losses. Like ot or not, it says what it says, which gives her the final decision. If she will not rate it at one hour, and you are required to have a one hour wall, somebody's gotta give. Good luck
It depends on what the meaning of "is" is.