Closed Thread
Results 1 to 3 of 3
Thread: Instantaneous Trip definition
  1. #1
    Join Date
    Aug 2006
    Saudi Arabia
    Posts
    94
    Exclamation Instantaneous Trip definition
    Can anybody tell me the definition of instantaneous trip?
    What is the trip time frame in general?
    Have a safe day
    Follow safety rules; protect your life...
  2. #2
    Join Date
    Feb 2003
    Wisconsin
    Posts
    7,950
    Quote Originally Posted by vinod View Post
    As fast as possible, with no intentional delay.
    The laws of physic pretty much prevent an activity from happening exactly instantaneously. Our industry uses this term to mean that the event is happening as fast as the mechanical operation can function.
    Just because you can, doesn't mean you should.
  3. #3
    Join Date
    Feb 2005
    Charlotte, NC
    Posts
    6,137
    Jim nailed it, IEEE definition is "No intentional delay"
    So the actual clearing time is based on the speed of the breaker itself. Usually 3-8 cycles, depending on the breaker type.