Originally Posted by
Jraef
For that reason (and the others I'll list below), this is usually done in the same enclosure, it's a bad idea to leave them separate. I would convert the MCC bucket to a feeder CB to feed a VFD panel that has the bypass starter in it, properly configured as below.
You CANNOT allow the line voltage to be applied to the load terminals of the VFD, otherwise all the magic smoke escapes immediately. For this reason, VFD manufacturers highly recommend using mechanically interlocked contactors on the output of the VFD that ensure that only one can be closed at any time. Electrical interlocking is required as well, but as we all know, contacts can weld and the consequence to that is the loss of a very expensive VFD.
So VFD bypass systems come in two "flavors": "2 contactor bypass" and "3 contactor bypass". What I described above is a 2 contactor bypass system, you just have 2 mechanically interlocked contactors, the bypass also has an OL relay of course (but there is another argument to be made on the location of that OLR see below). This allows the motor to run in the event of an inverter failure. But when that happens, you would have to shut down the entire system to remove and repair the VFD. A variant of this is to use a manual switch on the load side of the VFD that isolates the two circuits mechanically, typically a double throw safety switch or a rotary cam switch with 6 contacts.
A 3 contactor bypass adds a line isolation contactor ahead of the VFD so that if it becomes necessary to keep the motor running while the VFD is removed for repair, you can safely do so (under all the auspices of proper Arc Flash protection while doing hot work now of course). This is often done in critical equipment where automatic bypass is necessary. So consider that before deciding on a final configuration.
As to location of the OLR, something worth considering is what happens under OL conditions. If, for example, the motor was very hot while running under load with the VFD but the VFD then fails requiring you to switch to Bypass, the OLR in the bypass starter now "thinks" the motor is cold and may allow damaging current to flow before tripping. For that reason, many people prefer to locate the OLR down stream of the common connection, so it sees the motor current regardless of how it is powered. You would typically wire the OLR aux contacts only to the bypass contactor so the VFD is doing the protection by itself most of the time just to avoid confusion.