adding a sub panel

Status
Not open for further replies.

Rich2774

Member
I have an old 100amp 8 ckt fused panel I want to add a sub-panel . Would it be correct to come of the two lugs at the bottom of the bus bar with #6 and feed 50amp main breaker in the sub panel which is only 4ft away or can I just come off those lugs with #3s and go into the main lugs of the sub panel, Being that the main are 100amp fuses.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
What type of wiring method are you going to use?

Either one could work.

If you use the #6 you would need to follow the tap rules of 240.21(B) but that would be fairly easy to accomplish if the panel is only 4' away.

#3 THHN copper would have an ampacity of 100 amps at 75 degrees C. If you use an NM cable or a SER cable (Under the 2008 NEC) then you must calculate the ampacity in accordance with the 60 degree column.

Chris
 