i have been in this businees for 5 yrs and and 10 years including the whole elctrical side... i no what the code says about bonding the neutral and ground at the generator when not using a switched netral.however... i do not agree with this, and here is why- what happens when utility looses their neutral and u have floating neutral, now since ur ground and neutral isnt bonded at the gen, u will now have the same problem when it goes to gen power since utility is NOT bonded. does anyone agree with me? ever seen this happen?
Deja Vu, Roger and I had this conversation last night. No I do not agree. Reason being if you are on gen. power the gen. could care less about the utility neutral. The return current wants to go back to the source,being the gen. The simple way to look at the whole system in a non separately derived system is to pretend every thing past the main service disconnect is a sub panel. the gen is a sub, the transfer switch is a sub. The same rules apply that the neutral and EGC are only bonded in the first disconnecting means. After that every thing is separated to prevent unwanted currant on metal parts.