    2008 406.3(d)3(c)

    Could you guys give some examples and a little better description of 406.3(D)3(c)? 2008 NEC. Just making sure I understand it correctly. Thanks

  2. #2
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,529
    406.3(D)(3)(c) A non–grounding-type receptacle(s) shall be permitted
    to be replaced with a grounding-type receptacle(s)
    where supplied through a ground-fault circuit interrupter.
    Grounding-type receptacles supplied through the groundfault
    circuit interrupter shall be marked “GFCI Protected”
    and “No Equipment Ground.” An equipment grounding
    conductor shall not be connected between the groundingtype
    receptacles.
    You can remove an old two wire receptacle and replace it with a grounding type receptacle even if there is no grounding means at that box. But the circuit must be supplied by a GFCI and the receptacle labeled as stated.

  3. #3
    Join Date
    Sep 2008
    Posts
    101
    for example...could I have a GFCI receptacle at the first device location (instead of a GFCI breaker), and a grounding type receptacle at the next location (all properly identified) and be in accordance with the NEC...In your opinions of course?

  4. #4
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    21,838
    Yes, but it's important that you do not connect any EGC's to anything, not even to each other. Otherwies, a defective device could energize the case of another device.
    Code references based on 2005 NEC
    Larry B. Fine