Feeding a Single Phase 480 Transformer from a 3 Phase 3 Wire Panel

Status
Not open for further replies.
Hi,

I am looking at supplying a single phase 240x480 to 120/240 15kva transformer from an existing 3 pole breaker in a 3P 3W 480 panel board (ultimate upstream source is a grounded 480Y transformer) using only 2 phase wires with no neutral. The question I have is, does the code prevent me from doing this? I've been looking at section 250 and do not see where it would preclude doing this. What seems odd is that this new transformer will not have a neutral/grounded conductor on the high side (the low side would). Am I missing anything here?

Thanks,

Bohdan
 

mgookin

Senior Member
Location
Fort Myers, FL
Is it going to be utility owned (your profile says you are a utility engineer) or privately owned?
If utility owned, is it part of the utility's distribution infrastructure, or for use in their offices, etc.?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The code does not have an issue with that installation. It is just like any other feeder....you install the required circuit conductors and an EGC from the source to the load.
Of course you will need a grounding electrode and grounding electrode conductor for the secondary of the transformer.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Just be aware that there are a few breakers that require power flowing through all legs, which makes it difficult to use a 3 pole breaker for a 2 pole operation when the breaker is installed in a panelboard. Just make sure you ask this question of the breaker manufacturer first.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Just be aware that there are a few breakers that require power flowing through all legs, which makes it difficult to use a 3 pole breaker for a 2 pole operation when the breaker is installed in a panelboard. Just make sure you ask this question of the breaker manufacturer first.
I know that there are overloads that work that way but I am not aware of any breaker that works that way.
The UL White Book for "Circuit Breakers, Molded Case and Circuit Breaker Enclosures (DIVQ) says the following:
3-pole circuit breakers are suitable for use on 3-phase systems. A 3-pole breaker used in place of a 2-pole breaker on a 3-phase system, such as a 2-pole breaker used in a branch circuit that is actually two legs of a 3-phase system, is acceptable without the 3-pole breaker being specifically marked.
This applies to breakers listed under UL 489.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I know that there are overloads that work that way but I am not aware of any breaker that works that way.
The UL White Book for "Circuit Breakers, Molded Case and Circuit Breaker Enclosures (DIVQ) says the following:

This applies to breakers listed under UL 489.

I have not seen one in a long time but I did run across a MCCB once that had some kind of single phasing protection built into it. Might be what Jraef is talking about. I don't recall if it was something tied into a shunt trip or not though. Was a long time ago.
 
The code does not have an issue with that installation. It is just like any other feeder....you install the required circuit conductors and an EGC from the source to the load.
Of course you will need a grounding electrode and grounding electrode conductor for the secondary of the transformer.

Thanks. You refer to running the EGC. Since this is in a Generating Plant and we have a Ground Grid, is there any reason I cannot just attach to the nearest ground grid connection? In the 50 year old plants I typically work in, there are no EGCs run between panels or to motors, just the three phases. The conduits are all bonded and grounded.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I have not seen one in a long time but I did run across a MCCB once that had some kind of single phasing protection built into it. Might be what Jraef is talking about. I don't recall if it was something tied into a shunt trip or not though. Was a long time ago.

It's IEC designed breakers that do this, because in other parts of the would they use breakers as Manual Motor Starters by leaving the thermal trips adjustable instead of fixed. So as starters, the thermal elements are the OL and have the same differential current biassing of the trips as their bi-metal OL relays do. So they will require "looping through" all 3 poles. The thing is, a number of the breaker mfrs are now owned by EU based corporations (Siemens, Schneider, Eaton, ABB), who have been slowly integrating their IEC designs into their product mix here as "World Class" breakers.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The thing is, a number of the breaker mfrs are now owned by EU based corporations (Siemens, Schneider, Eaton, ABB), who have been slowly integrating their IEC designs into their product mix here as "World Class" breakers.
If the breaker is listed to UL489, it makes no difference if it is a EU design.

Panel breakers, often used internal to equipment, are rarely encountered as feeder and branch breakers in Switchboards and Panelboards.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Thanks. You refer to running the EGC. Since this is in a Generating Plant and we have a Ground Grid, is there any reason I cannot just attach to the nearest ground grid connection? In the 50 year old plants I typically work in, there are no EGCs run between panels or to motors, just the three phases. The conduits are all bonded and grounded.
If you are installing to the NEC, 250.30(A)(4) specifies the required grounding electrodes.

As far as the EGCs, metallic conduit is permitted to serve as the EGC.
 