    Overhead Service mast

    Trying to find code reference on allowable material for service mast riser. Always required rigid conduit, but can't seem to find code to back it up. This might be a POCO requirement. Any suggestions on where to find code reference other than 230.28. Thanks

  2. #2
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    16,795
    You got it!

  3. #3
    Join Date
    Sep 2003
    Location
    Santa Fe, New Mexico
    Posts
    181

    Overhead Service mast

    The requirement of the use of metal conduit is generally a utility requirement.
    The Code in 230.54 was the requirement for the use on cable and raceway.
    "The problems that exist in the world today cannot be solved by the level of thinking that created them."

  4. #4
    Join Date
    Feb 2003
    Location
    Portage, Indiana NEC: 2008
    Posts
    9,645
    Quote Originally Posted by inspector 102 View Post
    Trying to find code reference on allowable material for service mast riser. Always required rigid conduit, but can't seem to find code to back it up. This might be a POCO requirement. Any suggestions on where to find code reference other than 230.28. Thanks
    just apply 230.28 to 230.43 and you will have the only available requirement in the NEC, but almost all utility's will have a standard that will apply if you want them to hook up the electric.

    Also remember 230.28 only applys if the service riser mast supports the service drop conductors, if the drop is attached to the side of the house then only 230.43 applys, and of course the utility standard.
    Last edited by hurk27; 08-20-10 at 09:14 PM.
    Wayne A. From: N.W.Indiana
    Be Fair, Be Safe
    Just don't be fairly safe

  5. #5
    Join Date
    Feb 2003
    Location
    Portage, Indiana NEC: 2008
    Posts
    9,645
    I went to war with a local inspector who tried to stop me from using PVC as a riser pipe on a house where the drop was supported by the house, well he couldn't by state code, so he tried to get the utility to put in their standards to not allow PVC, so I called the Indiana utility commission and they told the utility that if they want to pay for the extra cost of using RMC instead of PVC then they would be more then welcome to require RMC, well you can guess how far that went. if they can not prove there is any safety problems with a wiring method and they are not footing the bill, then they have no right to dictate a wiring method that is allowed by code.

    I use PVC because not only is it safer, it is much easier and faster to restore power to a house when a tree has taken the service down, with PVC much less damage is done and it will usually snap off right at the male adapter leaving the male adapter to protect against having the un-protected service wire from shorting out to the meter can, or shorting out from the riser pipe being bent over, or the meter can from being ripped off the wall.

    I don't care how well you try to prevent a service from being torn off a building, a tree limb weighing 500 to 1,000 pounds will not stop till it hits the ground, your not going to prevent it, so the best way is to allow it, but in the safest way possible, sure I would like to see utility's to use a pull away type connection at the pole, but your not going to get them to spend the money, so I just use a method that is easy to repair and get power back on for the least amount of cost to the owner.

    I had one house that had many old oak trees in his yard that at some time in the past two or three times a year a limb would come down and tear out the service drop, the home owner got creative (or so he thought) and had the electrician bolt through the gable wall and through a 4x4 that went all the way across the gable end of the attic, when one of the heavy oak limbs came down it not only took the service off the wall but ripped out the entire end of the house, you could look right in and see inside, over $70,000 dollars in damage, now try to explain that to your insurance company. he had heard of my easy break-away type install and had me use the PVC method (after they rebuilt the wall)
    Last edited by hurk27; 08-20-10 at 09:41 PM.
    Wayne A. From: N.W.Indiana
    Be Fair, Be Safe
    Just don't be fairly safe

  6. #6
    Join Date
    Feb 2003
    Location
    Portage, Indiana NEC: 2008
    Posts
    9,645
    Quote Originally Posted by inspector 102 View Post
    Trying to find code reference on allowable material for service mast riser. Always required rigid conduit, but can't seem to find code to back it up. This might be a POCO requirement. Any suggestions on where to find code reference other than 230.28. Thanks
    102 if I remember right, your over around South Bend area, and have NIPSCO also, if so then if they try to inforce this dumb (no PVC rule) let me know, or call the Indiana utility commision, our state AHJ has already been in touch with them about this issue.
    Wayne A. From: N.W.Indiana
    Be Fair, Be Safe
    Just don't be fairly safe