    Practicable Limits to GFCI Recept Protection

    What are limits of downstream protection provided by 20A GFCI receptacles? Is GFCI recept. protection limited by distance from GFCI recept. to protected outlet? I have tried manufacturer's websites but haven't found pertinent info.
    I've done service calcs. (i.e. 180 v-a per single/multiple recept. per yoke, 90 v-a per receptacle in Plugmold, etc.). I've figured in branch-circuit load, wire size, voltage drops and OCPD's. I've read and re-read the 2008 NEC.
    Excluding requirements by local codes, and issues of the local AHJ, nothing seems to specify the max. number of downstream receptacles I can protect with a 20 amp GFCI recept. in unfinished basements, garages, outbuildings, etc.

    What is the practicable limit in terms of (1) How many downstream outlets can be protected and (2) How many feet from the GFCI can the last protected outlet be?

  2. #2
    Join Date
    Feb 2003
    Location
    N.C.
    Posts
    15,064
    Quote Originally Posted by reddy kw View Post
    What is the practicable limit in terms of (1) How many downstream outlets can be protected
    As many as you want.

    Quote Originally Posted by reddy kw View Post
    and (2) How many feet from the GFCI can the last protected outlet be?
    This would be a manufacturers issue, if the manufacturer doesn't address it, then there is no distance however, at some length there will be enough leakage to make the decision for you.

    Roger
    Moderator

  3. #3
    Join Date
    Aug 2010
    Location
    Mudville, upstate New York.
    Posts
    39
    Quote Originally Posted by roger View Post
    As many as you want.

    This would be a manufacturers issue, if the manufacturer doesn't address it, then there is no distance however, at some length there will be enough leakage to make the decision for you.

    Roger
    Thanks for the reply, Roger. That's what I though.
    I've heard about limits on GFCI receptacles for years, in non-NFPA/NEC books. Many electricians seem to believe there are limits, but popular belief doesn't make it true.
    It makes it an urban myth.

  4. #4
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    16,796
    I recall years ago there being a limit on both the number and the distance some manufacturers placed on their GFCIs.

  5. #5
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    3,345
    I wouldn't imagine any mfr is going to give you a hard number, because it depends on a lot of factors beyond their control. Even if a 1000' run worked today, 10 years from now as the insulation begins its long slow slide into oblivion (like we all do), the GFI may pick that leakage current up some day. And also, lets say you put 50 receptacles down stream. Plug in 50 incandescent light bulbs and no problem. But make 40 of them CFLs and the cumulative effect of the small amount of leakage in each little SMPS inside of them can be enough for the GFI to notice and trip. So if the mfr gives you a number and you have nuisances cause by one of the above, they may have to stand by that number.

  6. #6
    Quote Originally Posted by Jraef View Post
    I wouldn't imagine any mfr is going to give you a hard number, because it depends on a lot of factors beyond their control. Even if a 1000' run worked today, 10 years from now as the insulation begins its long slow slide into oblivion (like we all do), the GFI may pick that leakage current up some day. And also, lets say you put 50 receptacles down stream. Plug in 50 incandescent light bulbs and no problem. But make 40 of them CFLs and the cumulative effect of the small amount of leakage in each little SMPS inside of them can be enough for the GFI to notice and trip. So if the mfr gives you a number and you have nuisances cause by one of the above, they may have to stand by that number.
    CFLs do not matter. It is only connected between neutral and hot, so leakage between the two will balance out, thus not detected.

    Problematic loads are grounded SMPS that uses triangular arranged filter capacitor

    N-||-G-||-H

    If the filter capacitor was 0.01uF, and you have 100 of these power supplies connected, you effectively have 1uF between hot and ground, which may conduct enough current to trip some GFCI.

    Another issue is inductive load that kicks back, such as magnetic rapid start and electronic ballasts with passive inductive power factor correction on front end.

  7. #7
    Join Date
    Mar 2007
    Location
    Southern Illinois
    Posts
    258
    Quote Originally Posted by reddy kw View Post
    What are limits of downstream protection provided by 20A GFCI receptacles?
    I always thought it was limited to the number of stickers in the box.

  8. #8
    Join Date
    Aug 2010
    Location
    Mudville, upstate New York.
    Posts
    39
    Quote Originally Posted by 480sparky View Post
    I recall years ago there being a limit on both the number and the distance some manufacturers placed on their GFCIs.
    480sparky-That's exactly why I started wondering about this. New GFCI instructions don't say anything about limits. I too remember seeing manufacturers suggesting limits years back (been on the job since '86, things have changed).
    Until 2003, I worked under NYC Electrical Code (at time, an ammended version of 1987 NEC). I got used to having maximum numbers for everything, like number of boxes on a circuit. Thought maybe there are limits for GFCI's.
    Had to re-learn everything when I moved upstate. Thanks.

  9. #9
    Join Date
    Jun 2003
    Posts
    5,559
    I know this is for a breaker, but if a breaker has a limit, you would think a receptacle would be similar:

    QOGFI3.pdf

    Steve

  10. #10
    Join Date
    Aug 2010
    Location
    Mudville, upstate New York.
    Posts
    39
    Quote Originally Posted by steve66 View Post
    I know this is for a breaker, but if a breaker has a limit, you would think a receptacle would be similar:

    QOGFI3.pdf

    Steve
    STEVE-Thanks! I think that's the citation I recalled. I expect limit to length of wire run would be similar for GFCI recept.