I have sub panels in three apartments,can i run SER through pipe from meter pack to sub panels?
I have sub panels in three apartments,can i run SER through pipe from meter pack to sub panels?
Not if the S
Let me ask this,is SER not allowed in pipe just like romex?
I have sub panels in three apartments,can i run SER through pipe from meter pack to sub panels?
I am not aware of a code section that says you cannot install SER or NM in a raceway. However if you are installing a raceway, why do you want to install a cable in the raceway? Why not just install single conductors in the raceway?
I understand that, but I don't see anything from the OP that suggests this would be an underground run.You can run SER in a raceway. You just can't run the raceway/conduit underground as SER is not allowed underground.
I understand that, but I don't see anything from the OP that suggests this would be an underground run.
Not if the SER goes underground