Transformer secondary

Status
Not open for further replies.

csa3825

Member
Does article 240.21 (C) (4) intend that 2 separate main breakers can be fed from a common transformer secondary so long as the conductors for each breaker have an ampacity equal to or greater than each main breaker rating/setting and the conductors originate outdoors?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
As long as the transformer has the required protection noted in Art 450.3
you can make your statement and exclude the word "outdoors" if you obey the corresponding tap rules.
In other words, a properly protected (primary) transformer can feed multiple OCP devices on the secondary as long as each is installed per 240.21(C) ___ tap rules.
(C)(4) simply removes any length restrictions {such as the 10 ft in (c)(2)}
provided the provisions of (C)(4) are met.
 

yired29

Senior Member
As long as the transformer has the required protection noted in Art 450.3
you can make your statement and exclude the word "outdoors" if you obey the corresponding tap rules.
In other words, a properly protected (primary) transformer can feed multiple OCP devices on the secondary as long as each is installed per 240.21(C) ___ tap rules.
(C)(4) simply removes any length restrictions {such as the 10 ft in (c)(2)}
provided the provisions of (C)(4) are met.

Table 450.3 (B) note 2 will limit you to six OCPD's
 