The problem with your thinking is that each individual load cannot be divided among the three phases. Each load must be supplied individually.
Each heater requires 66.56kva, or a 75kva 1ph transformer. Two such loads would each require a 75kva unit; three such loads, three units.
3 x 75 = 225.
Just because you eliminate one of the loads, does not lessen the required capacity each transformer secondary must be able to supply its L-L load.
A Delta transformer supplying a Delta load is basically three 1ph units supplying three 1ph loads, and they happen to share line conductors.
While the shared lines will see 1.732 times the load current, each transformer secondary will see only the individual load across its two lines.
So, each secondary must be sized for the load across it. The only way to get two 75kva secondaries in one case is a by using a 3-ph 225kva transformer.
Master ElectricianCode references based on 2005 NECLarry B. Fine
Electrical Contractor
Richmond, VA
Oops. See below.
Last edited by LarryFine; 10-06-10 at 06:12 PM.
Master ElectricianCode references based on 2005 NECLarry B. Fine
Electrical Contractor
Richmond, VA
Last edited by hurk27; 10-06-10 at 07:34 PM.
Wayne A. From: N.W.Indiana
Be Fair, Be Safe
Just don't be fairly safe
What are the 320 amp loads that apparently can not be balanced across the three phases? Being able to balance across all three phases will allow for a smaller transformer, feeders, switchgear, and so on.
Some have mentioned heaters, but the OP did not mention what the load actually is.
For a given total load, yes. But, we're not talking about a bunch of small loads we can move around. This is two individual loads, each of which will be connected between two lines, i.e., across one phase.
The load current for each piece of equipment is 320a (even if intermittently.) Each source's phase must be able to supply that. That fixes the size of each phase's transformer to 75kva. Three of those is 225kva.
It looks like scott said it first in post #8.Some have mentioned heaters, but the OP did not mention what the load actually is.