Page 1 of 2 12 LastLast
Results 1 to 10 of 16
Thread: E-stops
  1. #1
    Join Date
    Oct 2010
    Posts
    4
    E-stops
    I have several old school mechanical assembly men that are used to having their e-stops wired so that when pushed in (activated) there is no light and when pulled out (de-activated) is lit up. My schooling and understanding of NEC code is that the e-stop should not be lit up if pulled out (de-activated) and if pushed in (activted) should be lit up red indicating a e-stop condition is present. Could someone else weigh in here and clarify this?
  2. #2
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    The NEC is silent on this.
    I also think it would be a bad idea to try to change what they are used to.
  3. #3
    Join Date
    Oct 2010
    Posts
    4
    So basicaly its up to the user to determine what they want the red e-stop light to indicate? Sounds confusing and I would think that there would be some type of code on this topic so that all machines with e-stops would fall into the same type of operation no matter who built it.
  4. #4
    Join Date
    Jan 2008
    Southern Maine
    Posts
    374
    one problem with an estop ligting up when activated is "what if the lamp is burned out", if the machine is getting ready to run and the lamp is out the operator may note this and put in a request for a work order to change the lamp. And I agree with iwire unless its an issue don't change it some may use that as a toubleshooting tool and though it can be overcome why mess with what has worked unless you have too.
  5. #5
    Join Date
    Mar 2009
    Big Easy
    Posts
    295
    Quote Originally Posted by iwire View Post
    Iwire is correct, changing what they are use to will only confuse everyone, or worse, some one way some the other.
    I've seen at a facility Green used for Motor Running and at another Green for Motor Stopped.
    Best to stick to the convention used for the site.
    How about circuit breaker position lights...We do Red Closed; Green Open.
  6. #6
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Quote Originally Posted by brewerinc View Post
    I am not really saying that, all I am saying is that is not what the NEC addressees'.
    The NEC will tell us how we have to wire the E-stops but not where to put them or how they will operate.
    I think there is a good chance it would be addressed in NFPA 79: Electrical Standard for Industrial Machinery
    http://www.nfpa.org/aboutthecodes/Ab....asp?DocNum=79
    There are some members here that know NFPA 79 very well and they may be able to help you more than I can.
  7. #7
    Join Date
    Nov 2003
    Roanoke, VA.
    Posts
    4,348
    I agree, NEC does not adress this.
    Nor would I try to change what they are used to.
    What you are proposing makes sense, but what if the bulb's filament had broken from vibration or some other reason since it was last operated? How would you know what E-stop had been activated?
    The way it is now only two things could make the bulb go out. Bad bulb or an E-stop activated.
    We often design our alarm circuits normally closed to open on alarm that way even if it is only a broken wire we will get an alarm.
  8. #8
    Join Date
    Jan 2008
    Southern Maine
    Posts
    374
    I agree with you on keeping things common but light or no light does not really influence the safety aspect of an estop. With all the different types of switching used in estop circuits it would not work to make all have lights cause some are not even that type of switch could be a micro switch if there is a jam up between some rollers or something.
    I did not see anything in the code on your question and can't think of any reason for there to be, unless it was an industry standard that all estops have a light but doubt that will be the case.
  9. #9
    Join Date
    Mar 2009
    Big Easy
    Posts
    295
    This is the colors from NFPA 79:
    RED - Danger or alarm, abnormal condition requiring immediate attention
    YELLOW (AMBER) - Attention, caution / marginal condition. Change or impending change of conditions
    GREEN - Machine ready; Safety
    WHITE - Normal Condition Confirmation
    BLUE - Any function not covered by the above colors
  10. #10
    Join Date
    Mar 2009
    Big Easy
    Posts
    295
    Quote Originally Posted by qcroanoke View Post
    If the E-stop is a mushroom head maintained type Pushbutton, Push to Trip, the one Pushed In would be the E-Stop that activated the trip. If the E-Stops are momentary than you couldn't tell. That of course is if all is hardwired. If they are wired to a PLC than any kind of capture of the events could be done.