C-10 test question - California

Status
Not open for further replies.
Sorry folks, I do not remember the complete question format or all of the multiple choice answers. Hope for the best and possibly some expert answers.

1. GFCI distance from inside the pool wall?
A) 6 Ft
B) 8 Ft
C) 10 Ft
D) 12 Ft

2. What is the maximum voltage for batteries put in series in residential?
A) 30V
B) 60V
C)
D)

3. How many 20A/120V outlets for continues light load 15KW?


4) As per title 24, at what number of outside lights photo sensors should be used to operate them?
A) 0


5) After a residential solar system was installed, customer complaint that the messages are recorded with a disturbance noise, is the problem because of?
A) Inverter
B) Telephone Line

6) 30A load berried in PVC in concrete should be at
A) 12 Inches
B) 36 Inc
C) 48 Inc
D) 6 Inc

7) Conduit run from inside the house to the outside, what is the best way to protect inside wires from moisture?
A) Special potty paste

8) Subcontractor electrician noticed on the walk through that the main panel is designed under size and was approved by the inspector. Whom should he contact?
A) Inspector
B) Contractor
C) Building owner

9) Under ground outlet found to be missing ground wire, the electrician must?
A) Install ground rod
B) Rewire ground wire to the main panel
C) Ground to the neutral
D)

10) Flood equipment should be on site before the work could start?
A) 25%
B) 75%
c) 100%

11) Roof flashing on a solar job is used to?
A) Stop rain
B) Stop dust

12) What type of conduit (Dust proof) should be used in a grain ware house?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Are these questions you missed? Tell us what you think the answers are and how you came up with the answers and we can help after that.

Roger
 

westernexplorer

Senior Member
Well, if your not even going to try and answer the questions and show some work, then I"m not about to help you.... You have to put some effort into this career and if you want to carry a License in your pocket that says you are COMPETANT... then you will have to earn it. I'm not going to do the work for you...
 

cbadelect

Member
"I am also looking to take the c 10 exam any good ideas on study books etc"

This is a classic case of "You can lead a horse to water but you can't make him drink"

joking aside I would check out www.mikeholt.com
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
1. GFCI distance from inside the pool wall?
A) 6 Ft
B) 8 Ft
C) 10 Ft
D) 12 Ft

I believe you will find the answer in art. 680.22(3) or (4)

2. What is the maximum voltage for batteries put in series in residential?
A) 30V
B) 60V
C)
D)

Article 690.71(B)

3. How many 20A/120V outlets for continues light load 15KW?
I think they want how many 20 amp circuits for continuous lighting. This is a bad question but if you get load each cir. to the max then you would take 20 amps multiplied by 120 volts and get 2400watts.

Now for continuous load take 80% of the 2400 watts and divide that into 15000 watts.

4) As per title 24, at what number of outside lights photo sensors should be used to operate them?
I know nothing of Calif title 24 law.


5) After a residential solar system was installed, customer complaint that the messages are recorded with a disturbance noise, is the problem because of?
A) Inverter
B) Telephone Line
I have no idea-- certainly the telephone can be a problem....


6) 30A load berried in PVC in concrete should be at
A) 12 Inches
B) 36 Inc
C) 48 Inc
D) 6 Inc

Look at Table 300.5


7) Conduit run from inside the house to the outside, what is the best way to protect inside wires from moisture?
A) Special potty paste
I don't know which is the best without choices. :)

Someone else can do the rest.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Sorry folks, I do not remember the complete question format or all of the multiple choice answers. Hope for the best and possibly some expert answers.

1. GFCI distance from inside the pool wall?
A) 6 Ft
B) 8 Ft
C) 10 Ft
D) 12 Ft

2. What is the maximum voltage for batteries put in series in residential?
A) 30V
B) 60V
C)
D)

3. How many 20A/120V outlets for continues light load 15KW?


4) As per title 24, at what number of outside lights photo sensors should be used to operate them?
A) 0


5) After a residential solar system was installed, customer complaint that the messages are recorded with a disturbance noise, is the problem because of?
A) Inverter
B) Telephone Line

6) 30A load berried in PVC in concrete should be at
A) 12 Inches
B) 36 Inc
C) 48 Inc
D) 6 Inc

7) Conduit run from inside the house to the outside, what is the best way to protect inside wires from moisture?
A) Special potty paste

8) Subcontractor electrician noticed on the walk through that the main panel is designed under size and was approved by the inspector. Whom should he contact?
A) Inspector
B) Contractor
C) Building owner

9) Under ground outlet found to be missing ground wire, the electrician must?
A) Install ground rod
B) Rewire ground wire to the main panel
C) Ground to the neutral
D)

10) Flood equipment should be on site before the work could start?
A) 25%
B) 75%
c) 100%

11) Roof flashing on a solar job is used to?
A) Stop rain
B) Stop dust

12) What type of conduit (Dust proof) should be used in a grain ware house?

are these actual test questions from the CSLB test?
Wow I sat on test writing before some of these questions are pretty abiguous.

Flood Equipment on site. Huh how is this the responsibility of the contractor and how is this something that can can prevent the EC from doing his work?
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
There absolutely is!
when I attended the test writing workshop there was also papers to sign to that affect.
I don't know how the schools get the questions.
 