    Can someone explain to me why phase to phase voltage is multiplied by radical 3 in a three phase system? I just asked my trig teacher and he couldn't help!
  2. #2
    Join Date
    Apr 2006
    Aurora, Illinois
    Posts
    72
    In a 3 phase wye system, the voltage measured line to line is not the
    sum of the phase voltage, because the voltage potential are out of phase by 120 degrees.
    Bottom line: if you are doing this for money, do it right or walk away.
  3. #3
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    22,627
    Draw a Y with three equal-known-length and equally-spaced arrows. Now, measure the distance from arrowtip to arrowtip, as the side of an equilateral triangle, and compare it to the arrow length.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  4. #4
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by wankster View Post
    Sinusoidal waveform formulas:
    L1-N voltage = cos(ωt)
    L2-N voltage = cos (ωt - φ)
    L1-L2 voltage = cos(ωt) - cos (ωt - φ)
    where:
    ω = angular frequency, i.e. 36060cycles/sec = 21,600/sec
    t = time in seconds
    φ = phase difference, here it is 120 or (120/180*pi) radians
    When you plot out the last waveform, you will find:
    L1-L2 voltage = √3 cos(ωt - 330)
    I will have achieved my life's goal if I die with a smile on my face.
  5. #5
    Join Date
    Mar 2006
    Westchester County, New York
    Posts
    8,221
    You may be thinking of the Square Root of 3, which is 1.732 - 3 phase multiplier.
    Instructor, Industry Advocate
  6. #6
    Join Date
    Nov 2004
    Posts
    3,172
    Quote Originally Posted by LarryFine View Post
    Isosceles triangle maybe?
    Don't mess with B+!
    (Signal Corps. Motto)
  7. #7
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by rattus View Post
    No question here... isoceles triangle definitely!
    120 at the vertex of the equal sides; 30 at the vertices of the equal sides with the unequal side. The relationship can be depicted as two back-to-back 30-60-90 triangles. As trig goes, the relationship of the long leg to hypotenuse is (√3)/2. So two long legs ios √3 times either hypotenuse.
  8. #8
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Supporting graphic...
  9. #9
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,874
    Quote Originally Posted by Pierre C Belarge View Post
    The OP said "radical 3." The term "radical" is equivalent to "square root of."
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  10. #10
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,874
    Send me a PM with your email address. I can send you a trigonometric derivation of the formulas for power in single phase and three phase systems. Give them to your trig teacher, and let us know what he says.