multiple seu cables in the same sleeve

Status
Not open for further replies.

GerryB

Senior Member
I know it is common practice and usually allowed to sleeve seu or ser cable for the service. Today I saw 4 seu cables for a multifamily in one 3 " sleeve. Is this a violation? We always do them individually.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I know it is common practice and usually allowed to sleeve seu or ser cable for the service. Today I saw 4 seu cables for a multifamily in one 3 " sleeve. Is this a violation? We always do them individually.

Not a violation but it's possible that derating of the conductors would apply,
 