MiElectrician

Member
Location
mi
I do have a 90 MC connector going through it the stainless, but other than that nothing, and if I drill a hole in the backing plate of the dryer to install a ground it'll make a place that could energize the stainless steel.
 

iwire

Moderator
Staff member
Location
Massachusetts
I would not worry about grounding the metal recess, I would just make sure the dryer is grounded as it should be.

The 90 is grounded by the MC armor.

It does get a bit interesting as in general MC is not allowed to be used with plastic enclosures but hand dryers are not really enclosures covered by article 314.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
It does get a bit interesting as in general MC is not allowed to be used with plastic enclosures but hand dryers are not really enclosures covered by article 314.
I didn't know this. Carlon, I believe, makes a plastic box with a rear knockout.
Huh? What does that have to do with MC?
 

MiElectrician

Member
Location
mi
I was unaware of 314.3. I'm glad this doesn't fall under it. I wouldn't be comfortable running Romex in that block and through the stainless steel recess. Thanks for the advice.
 