Thread: Old work ceiling box

  1. #1

    Old work ceiling box

    Is it illegal to use an old work ceiling box to support a light fixture?
    The only support is the wings on the sheetrock. I think you should only use them for smoke detectors.

  2. #2
    Join Date
    Aug 2010
    Location
    Ma
    Posts
    1,865
    Quote Originally Posted by Electrical Al View Post
    Is it illegal to use an old work ceiling box to support a light fixture?
    The only support is the wings on the sheetrock. I think you should only use them for smoke detectors.
    If it is just a regular light fixture i dont see why not

  3. #3
    Join Date
    Feb 2003
    Location
    Mike P. Columbus Ohio
    Posts
    3,351
    Quote Originally Posted by Electrical Al View Post
    Is it illegal to use an old work ceiling box to support a light fixture?
    The only support is the wings on the sheetrock. I think you should only use them for smoke detectors.
    One example:

    "The B618R is a round old work outlet box and is not listed for fixture support in
    the ceiling. Only approved ceiling boxes are allowed to support fixtures in the
    ceiling. These boxes will be permitted to support a minimum weight of 50
    pounds. The B618R can be used in the ceiling as a junction box. Do not hang a
    fixture from it since it relies on the strength of the ceiling itself."

    From: http://www.carlon.com/FAQs/FAQ-ZipBoxes.pdf
    Inspector Mike
    ESI

  4. #4
    Join Date
    Aug 2010
    Location
    Ma
    Posts
    1,865
    Quote Originally Posted by jxofaltrds View Post
    One example:

    "The B618R is a round old work outlet box and is not listed for fixture support in
    the ceiling. Only approved ceiling boxes are allowed to support fixtures in the
    ceiling. These boxes will be permitted to support a minimum weight of 50
    pounds. The B618R can be used in the ceiling as a junction box. Do not hang a
    fixture from it since it relies on the strength of the ceiling itself."

    From: http://www.carlon.com/FAQs/FAQ-ZipBoxes.pdf
    Thanks for the link mike
    I did not know that about the blue boxes thats good info:grin:

  5. #5
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    4,941
    Quote Originally Posted by Electrical Al View Post
    Is it illegal to use an old work ceiling box to support a light fixture?
    The only support is the wings on the sheetrock.
    If the box is the T&B 618R or 618RP, the round plastic rework box is not listed for fixture support. Take a look at the bottom of page eleven of these catalog pages.

    If you're using another manufacturer's box, look up the info at the manufacturer's site.
    Another Al in Minnesota

  6. #6
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    4,941
    Ah, I see Mike got there first.
    Another Al in Minnesota

  7. #7
    Join Date
    Apr 2007
    Posts
    848
    The boxes we use are marked for fixtures up to 6lbs
    The more I learn the less I seem to know....

  8. #8
    Join Date
    Feb 2003
    Location
    San Jose, CA
    Posts
    1,069
    Quote Originally Posted by jwjrw View Post
    The boxes we use are marked for fixtures up to 6lbs
    What boxes do you use?

    Most round old work boxes are listed to support fixtures (10-15 lbs) in walls but I have never seen one listed to support fixtures in ceilings.
    Curt Swartz
    Electrical Contractor

  9. #9
    Join Date
    Feb 2003
    Location
    Mike P. Columbus Ohio
    Posts
    3,351
    Quote Originally Posted by al hildenbrand View Post
    Ah, I see Mike got there first.
    I get lucky every now and again. I am just happy someone agreed with me once!
    Inspector Mike
    ESI

  10. #10
    Join Date
    Feb 2003
    Location
    Boston, MA
    Posts
    6,856
    Quote Originally Posted by jxofaltrds View Post
    One example:

    "The B618R is a round old work outlet box and is not listed for fixture support in
    the ceiling. Only approved ceiling boxes are allowed to support fixtures in the
    ceiling. These boxes will be permitted to support a minimum weight of 50
    pounds. The B618R can be used in the ceiling as a junction box. Do not hang a
    fixture from it since it relies on the strength of the ceiling itself."

    From: http://www.carlon.com/FAQs/FAQ-ZipBoxes.pdf
    I better tell people to start buying heavier fixtures.
    There are two kinds of people - those smart enough to know they don’t know, and those dumb enough to insist they do.-----Margery Eagan

    Open shop since 1988