Results 1 to 3 of 3
Thread: low voltage (shielded) wires and line voltage in same conduit?
  1. #1
    Join Date
    Mar 2009
    N of Anchrage, AK
    Posts
    172
    Can I run low voltage shielded control wires in the same conduit as line voltage control wires?
    The air handling unit we are to wire is 3ph 480. This is stepped down to 115v for 8 control wires, and the 115 if further stepped down to 24v for 2 shielded control wires. The drawings call for one pipe from the wall mounted controller to the ceiling mounted unit. Can I in this instance run line and low voltage in the same pipe?
    That is, is the shielding on the two wires protecting them from induced current (which is my understanding as to why we don't combine line and low voltage wiring in a box without a barrier)?
    Thanks for any comments.
    Howard
    "You don't know the character of a man until there is not enough." Dr. Jack Letts, MD
  2. #2
    Join Date
    Feb 2003
    Illinois
    Posts
    23,544
    If the 24 volt is an Article 725 Class 2 circuit it cannot be run in the same raceway as the power. 725.136
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  3. #3
    Join Date
    Mar 2009
    N of Anchrage, AK
    Posts
    172
    thanks
    Thank you, Don. I did a little hands-on research and found that the mfg. had put the 8 control wires in a 3/4 in. flex, and the two shielded wires separately in a cable. We'll just have to zip-tie the cable to the emt with the control wires. Live and learn: don't take the engineers plans as the final word.
    Howard
Posting Permissions
  • You may not post replies
  • You may not edit your posts