I saw these two panels today while doing a rough inspection. I was told I don't know what I am talking about. :roll:
This does not appear to be the service disconnecting means so having the neutral bar being connected to the cabinet would be a violation of 250.142(B).
Chris
Well , seems you are any more picky then we are. Assuming mains outside this is way off. If there are no mains then we have parallel neutrals. Either way something is wrong.I saw these two panels today while doing a rough inspection. I was told I don't know what I am talking about. :roll:
These are feeders and I was talking about the GC and the EGC being swapped. As well as the bonding jumper being installed. The electrician was a little upset due to the fact I found several other violations and stated there would be a re-inspection fee. If it was just the panels I would have waived the fee and looked at them on the final but there were other issues with the rough as well. He has already called my boss to complain, good luck with that.
I saw these two panels today while doing a rough inspection. I was told I don't know what I am talking about. :roll:
This is electricity 101--
Couldn't really tell from the picture, but it looked like they didn't use anti-oxidant either.