It's the air movement.

Originally Posted by
brantmacga
i may come up there and do some work just to have this argument.
i've had one inspector call me out on it; i told him find a dictionary and get back to me. job passed.
anyhow, like i said, if their intent was to include returns, then it should be worded as such.
until then, i won't be convinced otherwise.
i suppose one could say the return is "supplying" a forced air system; i'm not buying it though.
This may be just around here but the Fire Marshall explained it in a class many years ago that the distance was because of the air movement involved with a forced air HVAC unit. To close to the supply and and it blows the smoke away from the detector, to close to the return it can suck the smoke into the unit before setting off the alarm. Either way it would take more smoke build up to activate the detector than if it was away from the vents.