Results 1 to 4 of 4
Thread: NEC 300.4(E) Exception & NEC 358.12(1)
  1. #1
    Join Date
    Oct 2008
    Brooklyn, NY
    Posts
    884
    NEC 300.4(E) states that where RMC and IMC are installed under metal corrugated sheet roof decking, the 1-1/2 inch clearance is not required. I was wondering why EMT or any other metal raceway is not included in this exception. NEC 358.12(1) states that EMT is not permitted to be installed where subject to physical damage. My question is this. Would there be a real problem if EMT were installed under a metal corrugated roof without a clearance? Is EMT more susceptible to damage than RMC and IMC?
    Eric Kench, P.E.
    If it's not broken don't fix it
  2. #2
    Join Date
    Jan 2007
    New Jersey
    Posts
    1,023
    Yes and yes.
    Rick Napier
    Inspector and Instructor
  3. #3
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,670
    Those roofing screws will go right thru emt and you wouldn't even feel it.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,383
    Quote Originally Posted by erickench View Post
    It's been done that way for decades without much of a problem. Is it possible for a screw to penetrate it, yes, but IMO it's not very likely.