Senior Member
- Location
- NJ
If you had a few 2x2's fed from em panel and close by( about 5' away) you had exit lights fed from a different em panel would you combine the branch circuits in the same raceway(if it was a pipe job) or would you run separate conduit for the em lights and exits. Assuming they are (1) ckt each. Thanks