The circuit breaker box is bonded to the rest of the system via bonding jumper from the meter conduit lug to the panels neutral buss bar,
That would be a fail here. No such connection to the meter is allowed. Bonding must be done in the enclosure that houses the first disconnect. Panel bonding is usually done with the green screw supplied with the panel for just such use.
Cheers and Stay Safe,
Marky the Sparky
OSHA 1910.304(g)(2)(iv) "One phase conductor of a multiphase system where one phase is grounded shall be grounded"