Page 1 of 5 123 ... LastLast
Results 1 to 10 of 43
Thread: 3-Phase rectification & Ripple
  1. #1
    Join Date
    Jul 2009
    Ware Shoals, South Carolina
    Posts
    1,198
    I need a formula to calculate the AC ripple for an unfiltered 3-Phase Bridge ( 6 pulse ). The only formulas I can find are for circuits with a smoothing capacitor.
    Maybe I could just use an ungodly small capacitor for the calculation...?? :confused:
    The final intent of this exercise is to be able to measure the ripple to determine the health of the diode bridge. The supply is variable 0 - 300 VDC.
    Advise is a dangerous gift, even from the wise to the wise.
  2. #2
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by SG-1 View Post
    So what is/are the formula/s with the smoothing capacitor?
    I will have achieved my life's goal if I die with a smile on my face.
  3. #3
    Join Date
    Sep 2008
    UK
    Posts
    11,202
    If it's unsmoothed, perhaps an easier way to check if all the diodes are conducting would be to measure the DC output voltage of the bridge.
    Assuming it to be a full-wave six-pulse bridge, the output DC voltage should be 1.35 times the AC input voltage. Any non-conducting diodes will reduce the output voltage significantly.
    You can measure the AC ripple content but bear in mind that it predominantly at six times the fundamental frequency (probably 360Hz in your case) and is a fairly low voltage compared to the DC. The meter may not respond well to that. Anyway, for what it's worth, the RMS ripple for a six pulse bridge operating correctly is a bit over 4% of the DC voltage.
    One other thought. I've been in the power electronics game since before the Dead Sea reported sick. I can't ever remember a power diode to fail by going open circuit. The usual failed condition in my experience is short circuit. And that you can easily check with most standard multimeters.
  4. #4
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    22,758
    Quote Originally Posted by Besoeker View Post
    That's cute!
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  5. #5
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    I need a formula to calculate the AC ripple for an unfiltered 3-Phase Bridge ( 6 pulse ). ...
    .... Anyway, for what it's worth, the RMS ripple for a six pulse bridge operating correctly is a bit over 4% of the DC voltage.
    Don't know how accurate the formula is, I derived the formula myself... I did not reference any publications.
    FWIW, it yelds a waveform of about 6.7% p-p, which I imagine is pretty close to a bit over 4% rms.
  6. #6
    Join Date
    Sep 2008
    UK
    Posts
    11,202
    Quote Originally Posted by Smart $ View Post
    Altogether unnecessarily complicated and not right anyway.
    Peak voltage, Vp, as always is Vp = root(2) * Vrms
    Minimum is Vp sin (60) or Vp*root(3/2)
    So peak to peak is about 14% of maximum voltage.
    I suppose I have posted this before. It gives the waveform, the ripple, and the 6th harmonic content.
  7. #7
    Join Date
    Jul 2009
    Posts
    1,198
    I was using this website:
    http://www.electronics-tutorials.ws/diode/diode_6.html
    V (ripple) = ( I(load) / ( f(60hz) x #P (6) x C )) x V
  8. #8
    Join Date
    Jul 2009
    Posts
    1,198
    This one diode ejected it's anode. ( I have a picture, but my uploads fail since the forum changed. I am probably doing something wrong.) Others were shorted. This resulted in arcing on a variable auto-transformer.
    10 bridges ( 9 now) with 12 diodes per bridge & I would rather not open the cabinet, but I can.
    I am digesting the rest of your posts, good stuff. ( Yum )
  9. #9
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    When I stated 6.7%, my reference value was AC voltage peak to peak. Referenced to one bus of rectified voltage it would be double at 13.4%.
    Additionally, your formulas do not yield an instantaneous waveform. SG-1 did not specify what type of formula he was wanting. Plotted out, my formula's waveform is identical to yours.
  10. #10
    Join Date
    Sep 2008
    UK
    Posts
    11,202
    Actually, not quite right. It is 13.4% referred to the peak of the AC voltage. Not the DC.
    That sounds like an oxymoron.
    The formula yields an instantaneous value. The waveform is a time varying function, not an instantaneous value.